APC SUA2200RM2U Ultra Short Battery Life

Notice: Page may contain affiliate links for which we may earn a small commission through services like Amazon Affiliates or Skimlinks.

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
So I finally upgraded from a stand alone UPS to a nice rack mount one.
I got a SUA2200RM2U off ebay without batteries.

I had to put a lot of work into it, ordered the batteries, repaired the power cable, I also got the AP9631 Network Management Card.
Today it all comes together and its installed, and something just is not right.

It reports almost no load, but only a 6 minute run time with full capacity.

The battery bank I am sure is hooked up right, it has the correct voltage and everything.
From the management card I ran the run time calibration thinking it just needed to be calibrated and it was a false reading, but sure enough about 6 minutes and it was dying and the voltage dropped enough to end the test.

I am not sure if there is some other means of calibration or a setting I need to change, or if this can somehow simply be defective?

Also I should save this for another thread, but I am looking to get the PowerChute software setup for ESXi that was one of the main reasons for the Management Card short of having cool access to logs and status.

Here are the batteries I used.

Any help is greatly appreciated.
 

Blinky 42

Active Member
Aug 6, 2015
615
232
43
48
PA, USA
Does it report a load that lines up with what you expect for the equipment plugged into the unit?
How long does it run w/o any devices plugged into it with just the UPS's internal load on the battery?
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
Does it report a load that lines up with what you expect for the equipment plugged into the unit?
How long does it run w/o any devices plugged into it with just the UPS's internal load on the battery?
I think so I have to double check. I know the LED's show minimal load and my rack is only ~300w so that seems right.
It would not run much longer without anything connected.

I am thinking its probably a bad battery (or more than one) I hate to go pay the huge prices for a APC replacement battery pack kind negates all the savings and all the hard work I put into doing this myself.

I am not sure I can even remove the battery pack to test the cells without killing all my equipment, as I know the unit wont turn on without the battery connected, so I am not sure if it can be removed while it is running.

Building that cell was a pain... some of the cables are so short that its nearly impossible to fit it all together. If I have to rebuild it again I might want to see if I can find some longer cables.
 

Stephan

Well-Known Member
Apr 21, 2017
992
757
93
Germany
You probably need to reset one of the EEPROM constants back to factory, see here: APCUPSD User Manual

I think you have to remove the network card for this, otherwise the console port is disabled.

After battery has floated for 2-3 days check voltage of entire pack using a voltmeter and compare with what processor is seeing and telling you. There is a possibility to fix this, should electronics have drifted a little. See APC SmartUPS Battery Float Voltage Calibration

Floating voltage for entire pack in a 48V APC should be 54,54 volts (easy to remember) to prevent electrode sulfation, but not be too high to "cook" the battery within 2-3 years. In SU models this was controlled using resistors, in later models like SUA afaik you could change this programmatically using the "B" command (see SUA1500i - Unofficial APC UPS protocol).

Finally put a 40%-50% load like a 1000W space heater or two 500W lamps on the UPS and let it run until empty to recalibrate some other stuff in the UPS. Let me know if it worked.
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
You probably need to reset one of the EEPROM constants back to factory, see here: APCUPSD User Manual

I think you have to remove the network card for this, otherwise the console port is disabled.

After battery has floated for 2-3 days check voltage of entire pack using a voltmeter and compare with what processor is seeing and telling you. There is a possibility to fix this, should electronics have drifted a little. See APC SmartUPS Battery Float Voltage Calibration

Floating voltage for entire pack in a 48V APC should be 54,54 volts (easy to remember) to prevent electrode sulfation, but not be too high to "cook" the battery within 2-3 years. In SU models this was controlled using resistors, in later models like SUA afaik you could change this programmatically using the "B" command (see SUA1500i - Unofficial APC UPS protocol).

Finally put a 40%-50% load like a 1000W space heater or two 500W lamps on the UPS and let it run until empty to recalibrate some other stuff in the UPS. Let me know if it worked.
So I read the calibration papers, it says you can do manual aka with a load and let it drain, or from the network card you can run the calibration like I did the other day.

voltage reading on the status page and my volt meter looked good, it just dropped incredibly quick once I put it on battery, so I really do think it might be a bad cell.

I ordered a battery tester from Amazon that will be here tomorrow and I will test the batteries and see if I find a bad one.

I unfortunately do not have the console cable needed to do any of the cool console stuff. Also not sure why but my network management card is offline. I see a link light but it no longer has an IP address. I assume just pulling the card out and putting it back in will reset it rather than turning the whole unit off.
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
Reset the network management card and got back in.
These numbers do not look right for load. I have used P3 before on my rack and it draws between 200 and 300w.


Status
Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:29.7°C
Runtime Remaining: 5min
Power
Input Voltage:123.8 VAC
Output Voltage:123.8 VAC
Frequency:60.0 Hz
Load
Load Power:19.5 %Watts
Apparent Load Power:20.8 %VA
Load Current:3.3 Amps
Battery
Capacity:100.0 %
Battery Voltage:55.08 VDC
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
Still no luck.
Got the battery tester, all the batteries tested good.
Did the calibration run until it cut off and determined it needed to run on power again and then tested each battery with a volt meter and still was getting 12v+ per cell.

I think the issue here is the unit has a very high cut off voltage, in my reading I think it should be able to go down to as low as 42-43v before cut off safely but mine is cutting off in the 50's

I see nowhere i can configure this, even downloading the entire config file.
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
Just once more: You need a console cable and reset the battery constant to factory.
Ok I guess I will do this, no way to reach those commands via the NMC or SSH? What console cable to do I need exactly?

I have a USB to Serial adapter already for programing my ESP8266 and ESP32 MC's so I might be able to just use raw wire and a header on the board, or fashion some kind of external cable for it, but if its cheap enough I'll just get the right cable.
 
Last edited:

Stephan

Well-Known Member
Apr 21, 2017
992
757
93
Germany
My cable says "APC 940-0024D". I know of no way to reach the parameters via the card.

IMHO for longevity correct float voltage is much more important than brand. Sealed lead-acid is on its way out, next-gen products might all be LiFePo4. So no big innovations for any manufacturer to be expected. It is a very mature technology. Your 55V is already a bit on the high side. Yuasa for example wants 54,6, CSB even wants 54V as lowest float in a 48V pack. Personally I am using Effekta batteries and those want 54,4 on the low side of the spectrum.
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
the UPS reads it as 55v but with a multi meter I get less than that. Like 52, but that might not be a fully charged battery with the surface charge not removed. Id have to retest to verify after fully charging.
 

Dave Corder

Active Member
Dec 21, 2015
326
217
43
42
I use a DB9-RJ45 adapter wired to the Cisco console pinout on my APC UPS, and then a standard Cisco console cable with integrated USB adapter from my networking kit.

Examples:

 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
So I have a FTDI USB to serial on the way and a knock off APC cable from ebay wont be here for weeks though. I also found today a program that looks very promising called apc-fix.exe it seems like it can do what I need to do automatically. However I cant tell for sure if the "free" version vs the "full" version has any restrictions.

The setting I can change is the voltage constant once I get this, it should read my batteries voltage correctly after, but I do not see a setting for what voltage the batteries actually "cut off" and I still need to determine for sure what value to set.

There is a possibility that the batteries are the cause of the issue and that if I got some APC branded batteries it would just work. I think I see hints here and there, that this issue happens with self replacement batteries that are not in the same spec. Who would have thought? I mean they are all 12v batteries.

I dont understand how the equipment has such a hard time just reading voltage and acting accordingly.

I do have a cisco console cable, so might try your way just for fun. I had no idea that at its heart it was serial communication all the same. When I looked up the pin out for the APC cable it had shorts and stuff that I though might be required ontop of the ground, tx, and rx pins.
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
So I got this fixed I guess, found a pretty cheap USB to Serial Cable made for APC on Amazon (cheaper than buying the console cable and a USB Serial Adapter, and no wait like from ebay) was able to get in there and from days of research found how to change two key things.

The battery constant (Found two different possible values for my model) and the float voltage.

My float voltage was 54.5 at the meter and that is perfect so I left that alone, and I found a neat trick, that you just set the battery constant to FF (the maximum value) so you get the longest run time possible and it will still shut down based on voltage.

Now the one issue I have is my voltage and load readings are still wrong at the unit the 56.x volts and 20w load figures are very off, and my run time is way shorter than what I would have expected from this unit. However I guess thats just how it is and I maybe had unrealistic expectations.

One of those small UPS you buy from Best Buy or Amazon with a 1500VA rating last just as long if not longer.

Since I went thru so much trouble to get this working and figure it all out, I actually have a 2nd one on the way from ebay and I will see if it has similar results.

I also may "hack" one of these with deep cycle car/marine batteries. Now that I know how to tweak and change things I can use non standard batteries pretty easily.

I also got the console cable for the NMC just incase I need that for any reason.
 
  • Like
Reactions: StevenDTX

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
Might be time to retire these old dogs, I have 2 of them one on the server rack and one on my desktop.

I have had to do a battery rebuild 3x now, and I cant say if its because the margin of error for replacement batteries is so small, or all of them you can buy for a reasonable price are just garbage.

Currently my UPS for the server rack is saying battery failure, I just tested and I get full voltage that I should get on the battery and each individual cell.

So as much as I like these the constant issues over time and new tech being out now, what is a good recommendation for a replacement?
 

BoredSysadmin

Not affiliated with Maxell
Mar 2, 2019
1,067
440
83
My 2c - get an Eaton UPS. I bought it a while ago HP re-branded Eaton 1500VA UPS, and so far, it's been great.
Edit: The model is HP 1500 G4. I bought it as used in 2020 with used batteries - which still work fine. Had few power outages in last (over) 4 years and still running on original batteries unit came with.
Edit2:
Like this one: Hp R1500 G3 NA Uninterruptible Power Supply W/Battery Cables FREE SHIPPING | eBay
 
Last edited:

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
My 2c - get an Eaton UPS. I bought it a while ago HP re-branded Eaton 1500VA UPS, and so far, it's been great.
Edit: The model is HP 1500 G4. I bought it as used in 2020 with used batteries - which still work fine. Had few power outages in last (over) 4 years and still running on original batteries unit came with.
Edit2:
Like this one: Hp R1500 G3 NA Uninterruptible Power Supply W/Battery Cables FREE SHIPPING | eBay
Is that 1U? It looks like it in the pictures but it has to be 2U for the batteries i'd assume.

Ever get any advanced features working for it like network monitoring and email alerts? Some of the things I have now that I'll miss a bit.
 

BoredSysadmin

Not affiliated with Maxell
Mar 2, 2019
1,067
440
83
Is that 1U? It looks like it in the pictures but it has to be 2U for the batteries i'd assume.

Ever get any advanced features working for it like network monitoring and email alerts? Some of the things I have now that I'll miss a bit.
that one is definitely 1U. As for network monitoring, you could get NUT on RasPi (or similar SBC) - Setting up a NUT Server on your Raspberry Pi

Alternatively, get a model with native network management, like this one:
It's quite a bit more expensive, especially on shipping (unless you're near Plano,TX) but does include batteries
 

ViciousXUSMC

Active Member
Nov 27, 2016
274
147
43
41
That is not a bad deal for the G5 with batteries, I was looking at a G4 with batteries for almost the same, and most batteries are expensive that I am seeing on line.

Those network cards are EXPENSIVE and hard to find so its probably worth it for that alone.

Hopefully batteries can just be swapped and no crazy hacking nonsense like I had to deal with on the APC units.

So I will pick that one up and see how it goes, and it will be good to get another 1u of rack space back too :)

Just for something to tinker with, this G4 no batteries looked clean so got that as well.

Never can have too many UPS lol.
 
Last edited: