I just setup a bunch of SMX2000RMLV2U and SMX3000RMHV2U, and just installed fresh batteries in them this week (they're each showing about 135.2V-135.6V on the batteries), and I'm finding them drawing 3 amps each (@ 125V), and 1.4A @ 218V (for the HV models) with no loads attached! That's like 300-375 watts!
These are set in "Green Mode" which is supposed to be up-to 98% efficient (it doesn't do any buck/boost/voltage output regulation when on Utility power), and the batteries are showing 100% charge on every unit (they are brand new). 98% efficiency on a 2000W load would imply < 40W of "waste" power consumption from the UPS (which would be inline with my expectations). I'm seeing roughly 10X that!
It seems that the only explanation is that the UPSes are charging the batteries (despite them being full and reading at 100% charge on the UPS), which is it's own kind of worrying, because charging them at 200W+ for an extended period of time when they're already full sounds like a fast way to boil off electrolyte.
When I turn off the output section, the power use drops to about 1-2A @ 120V. Which implies a couple things:
1. Charging is only about half of the current being used when they're on, and the other half must be the UPS itself.
2. Despite not doing any buck/boost/power regulation/etc. (reminder, they're in Green Mode), they're taking something like 1.5A to produce no power at 120V? That seems far higher than expected for an idle UPS not doing any power regulation. It also doesn't jive with the theoretical 98% efficiency figure; where the UPS would be expected to "waste" only about 40W on a 2000W load...
Has anyone ever tested their APC Smart UPS X idle power consumption? Or encountered this kind of waste from a UPS with fresh batteries?
These are set in "Green Mode" which is supposed to be up-to 98% efficient (it doesn't do any buck/boost/voltage output regulation when on Utility power), and the batteries are showing 100% charge on every unit (they are brand new). 98% efficiency on a 2000W load would imply < 40W of "waste" power consumption from the UPS (which would be inline with my expectations). I'm seeing roughly 10X that!
It seems that the only explanation is that the UPSes are charging the batteries (despite them being full and reading at 100% charge on the UPS), which is it's own kind of worrying, because charging them at 200W+ for an extended period of time when they're already full sounds like a fast way to boil off electrolyte.
When I turn off the output section, the power use drops to about 1-2A @ 120V. Which implies a couple things:
1. Charging is only about half of the current being used when they're on, and the other half must be the UPS itself.
2. Despite not doing any buck/boost/power regulation/etc. (reminder, they're in Green Mode), they're taking something like 1.5A to produce no power at 120V? That seems far higher than expected for an idle UPS not doing any power regulation. It also doesn't jive with the theoretical 98% efficiency figure; where the UPS would be expected to "waste" only about 40W on a 2000W load...
Has anyone ever tested their APC Smart UPS X idle power consumption? Or encountered this kind of waste from a UPS with fresh batteries?