1. Introduction
I've recently been through the process of trying to modify the fan configurations of a number of my servers from the stock OEM configuration to something else to reduce the amount of noise they produce. These servers were often designed without noise output as a meaningful consideration, and introducing that as a constraint has some trade-offs. My initial approach was to buy as many of the largest, highest CFM fans that I could, work out a way to mount them, and see if system temperatures stabilised with these new fans installed.
This approach left a lot of questions for me - what were the trade-offs that I'd made in this bargain? Was I still able to use these servers under full load without damaging the hardware? Had I selected the right hardware? Did I get enough fans to cover the thermal load? Were they placed geometrically in the right positions? Would these fans be satisfactory when I increase the number of hard drives in the server? In some cases, these fans weren't cheap either, and so exploring multiple solutions was becoming prohibitive.
So I decided to take a more engineering-based approach to better understand the design and solution space, so that I could make active decisions around some of these trade-offs. To be specific, the trade-offs that exist in this space when selecting a new fan are:
This certainly isn't the only way to tackle this problem, but I thought others might get value from the process that I went through. If you enjoy over-engineering your homelab; this guide is for you!
Disclaimer: I have a background in physics and engineering but I'm not a HVAC engineer - I learnt a lot of this in the process of my exploration of the problem. There's every possibility I'm misinterpreting parts of the theory and how it should be used appropriately.
2. Concepts of air cooling performance analysis
There are two elements to air cooling performance as it relates to fan selection:
In a free stream of air, there is no system impedance. This is where the Max Airflow measurements are taken, and is often what's reported in performance summaries. That means that the maximum airflow metric may be a relevant to you if you're intending your cooling solution to operate in a largely sparse/unpopulated environment (think single CPU 4U/5U or ATX form factor systems, though it always depends on the specific system). If the system is densely populated on the other hand (think 1U and 2U servers, particularly if they have a lot of hot-swap HDD bays), this metric is likely less valuable. What you're interested in is the airflow (CFM) that can be achieved at the system impedance, and so inspection of a P-Q chart is imperative.
System impedance is made up of two elements:
On a fan specification summary data sheet, the "maximum static pressure" is also often cited, which is the system impedance (static pressure) at which the fan is unable to induce a flow of air (CFM=0). It is not possible for a fan to achieve its maximum airflow (CFM), and it's maximum static pressure at the same time. The airflow that a fan is capable of producing is determined by the static pressure of the system, and so performance of a fan is definitionally dependent on the system it is being used in and the role it is playing within that system (is it a case fan, a CPU fan attached to a heat-sink, a radiator fan?).
This is made a bit clearer by looking at the difference between placing two fans in parallel or in series (discussed later).
Note: I'm pretty inconsistent with units in this write-up. I have a strong preference for using SI wherever I can, but the resources and data around this are a bit of a mess. I've used SI wherever possible, except in the representation of performance where I've stuck to CFM and in H2O. Note that for the calculations to work you can't mix and match unit systems. For reliable results make sure you're only ever using SI when calculating quantities.
2.1 A note on determining system impedance
Having some kind of estimation of system impedance is critical to performing analysis this way. Without it, it's impossible to know where on the P-Q curve the system is and you have no basis for decision making. In order to get an estimate, the gold standard here would be to do this experimentally and take measurements of the system using a pitot tube and a manometer to properly characterise it. More generally though (in the absence of an ability to fully derive this experimentally), the system impedance follows the "square law", characterised by this equation:
where:
Given a system characteristic coordinate (P, Q) (from someone else's effort to characterise a similar system experimentally), we can solve this equation for K and then build up a system impedance curve. To illustrate:
Once we have K, we can substitute it back into the original equation for a sweep of Q values and plot the resulting P values. The utility of this relies on obtaining data from elsewhere, but this will be shown on graphs later using the limited information I was able to find.
2.2 How does placing fans in series or parallel affect cooling performance?
The general principle is discussed in the following sections.
2.2.1 Two fans in parallel
When two fans are placed in parallel, this primarily improves the airflow of the system. However, when compared to a single fan, it also sees a small improvement to static pressure performance, as demonstrated below:

As you can see, the system impedance curve intersects the parallel fan performance curve at both a higher static pressure, and it also produces a higher airflow. However, the intent of this configuration is to increase airflow in low static pressure systems, and the effect of this in the example above would have been more effective if the system impedance curve was lower.
2.2.2 Two fans in series
In contrast, when two fans are placed in series, this improves the ability for a fan system to operate with high system impedance. Like in parallel, we see an increase to both static pressure performance and airflow performance, however biased towards static pressure:

As can be seen, the system impedance curve intersects the fan system in series at both a higher static pressure and a higher airflow.
Both the concepts of parallel and series arrangements will be explored in the solution space later on to support selection.
3. Characterising the system
Before making changes to the system, it's good to understand how it currently performs, at least as the basis for evaluating alternatives, but also to better understand the designed-for performance regime.
The Brocade ICX7250-24P contains two Foxconn PIA040H12P 40x40x28mm exhaust fans arranged in parallel, each of which has a maximum air flow rating of 26.33 CFM and a maximum static pressure rating of 2.04 in H₂O.
In terms of the system impedance, I was unable to find any information specific to the Brocade ICX7250-24P, or any other Brocade product for that matter. This is considered a major limitation of this analysis. In fact, it was shockingly difficult to find any values for 1U servers more generally with any basis in reality. However, I did manage to find some for 1U and 2U servers that were produced by IBM and published in "Analysis of Airflow Distribution Across a Front-to-Rear Server Rack" (Radmehr et al., 2007):
There are a few limitations associated with using these values. A non-exhaustive list includes:
This current system performance is summarised in the following P-Q chart (fan characteristics digitised from data sheets):

Note that the single fan performance is only shown here for informational purposes. The total system fan performance is represented by the orange line. As can be seen, at the system fan curve intersects with the system impedance curve at (Q=49.3 CFM, P=0.2 in H₂O). Since these fan performance curves indicate airflow potential when operated at 12V (100% duty cycle), this means that the system designers anticipated that 49.3 CFM would be sufficient to keep the system within acceptable thermal thresholds when operating it at maximum load.
At idle, in Speed 1 (not the full speed shown above delivering 49.3 CFM), the system has the following measurements:
Demonstrating that the idle temperature is at approx 60°C. Observing the fan duty cycle in this configuration:
shows that these are spinning at ~6300 RPM. We know from the spec sheet that 100% duty cycle for these fans is 18000 RPM, so Speed 1 corresponds to ~35% duty cycle.
4. Understanding the thermal requirements
Before we get stuck into analysing different fans, it's useful to have a meaningful lens through which to view that performance. Namely, how much airflow do I actually need to cool my system? Armed with that information, we'll be able to identify the alternatives that are "good enough". Fortunately, the amount of heat produced by electronic components matches closely with the power consumed by the system, so we can derive the airflow requirements using the system power consumption.
4.1 Power Load
First, let's understand the requirement. We can look at the power consumption figures provided in the technical specifications for the Brocade ICX7250 series of switches, which provide the following consumption values for a few performance regimes (I assume 200VAC input here):
Note that the "Typical" configuration assumes that all ports have a PoE load and 10% traffic. The difference between this and the "Maximum" configuration is that the Maximum configuration has 100% traffic. In this case, PoE is obviously the biggest consumer of power.
Note: I've only included the PoE variants of the switches here because they are the most interesting. If you have a non-PoE variant, you should be able to follow the same process but your requirements will be far less constrained, so your performance will be impacted less by your fan selection.
4.2 Required airflow calculation methodology
The sensible heat equation gives us a model for understanding the trade-offs between power consumption, designed temperature rise and required airflow:
where:
This can be used a couple of ways:
4.3 Results
I've performed a sweep of parameters Q, hₛ and ΔT in the above equation to make the relationships a bit easier to visualise. The figure below shows how the airflow requirements vary for different heat loads, with different design temperature rises. I've also shown where the power load for the ICX7250-24P and ICX7250-48P lie on this chart. To read this, look at the CFM associated with the intersection point of these power loads and the desired temperature differential.

There are a few interesting insights to pull out of this:
To summarise:
To state the obvious, the other dimension that hasn't been discussed here is operating the switch in a manner that doesn't take it to its design load. Managing the amount of energy consumed is another way to bring down the airflow requirements without sacrificing the design temperature. To plan your cooling solution around some fractional capacity, simply take the intended power consumption and identify the airflow requirements at the ΔT of your choice. In this case, an easy win for users of the ICX7250-48P would be to adopt a policy of using some fraction of the total PoE ports. To illustrate, if you chose to only use 24 of your 48 ports with PoE, your requirements would relax to something approximating the ICX7250-24P.
5. Fan performance
Below are a selection of fans for comparison. These fans are a mix of:
In order to get a better view of how each of the candidate fans performed relative to each other, I digitised all of the performance charts that the vendors provide (shout out to Engauge Digitizer), and overlayed this with the system impedance curves described earlier to help guide our assessment of the performance regime of these fans that we should care about.

Note: Like-for-like performance should be compared at the points at which each fan intersects the "Typical 1U system impedance" curve, which follows a square law. You should not just compare values at the same static pressure; these are not comparable due to the dynamic pressure component of system impedance produced by the airflow itself.
We shouldn't read too much into this figure; these represent the single fan performance, and what we really care about is the total system performance. Having said that, it's exceedingly obvious just how much better the OEM Foxconn fans are than any of the other alternatives being evaluated, both from a pressure and airflow perspective. It's also surprising how the performance regime demonstrated by the "typical 1U system impedance" curve is so close to the maximal airflow performance of the fans. If this assessment of the system impedance is realistic, then the first order analysis described in the introduction is probably sufficient; comparing the max CFM values (and ignoring static pressure as a metric) is probably "close enough". Additionally, looking at the chart, the distance between the OEM fan and the next most performant stays roughly equidistant for the entirety of the profile.
As mentioned earlier, the default configuration for the ICX7250-24P is two exhaust fans arranged in parallel at the rear of the chassis. This is the baseline from which performance will be compared. In the case of the ICX7250-24P, there is an unused mounting point for a third fan, and usage of this should form part of the solution space. The following configurations will be assessed in the following section:
6.1 Single Foxconn fan
As can be seen in the single fan performance chart above, the usage of a single Foxconn fan would generate ≈26 CFM at the system impedance. This is a viable alternative, generating a ΔT ≈ 30°C at the maximum load of the ICX7250-24P, if a little hotter than I would prefer. This is also effective at reducing the sound output by (2 times quieter) at maximum load. However, another consideration is the noise when not loaded up to the maximum load. At Speed 1, these fans operate at 35% duty cycle. This generates 9 CFM from one fan, which is enough to support 128W of heat at ΔT = 25°C or 156W at ΔT = 30°C. I don't have any data to quantify the noise level at this duty cycle (I haven't been able to find noise/RPM curves for any of the fans assessed), but in my personal anecdotal experience it is too loud, and offers limited improvement over just keeping the stock configuration.
The following are the measurements I took after letting the switch reach a steady state with only a single fan:
So, ≈75°C at ~6300 RPM.
6.2 Two fans in parallel
As a reminder, the way to read the performance on the following chart is to identify the airflow generated at the intersection point of each fans curve and the relevant system impedance curve. I have also marked where the predicted temperature rise thresholds exist for the full load configuration of the ICX7250-24P. These thresholds will be different for the ICX7250-48P. In order to identify which fans meet the ΔT=25°C threshold, look at the fan performance curves that intersect the system impedance curve to the right of this threshold.
The legend in these charts shows each fan model in a unique colour. I appreciate these charts are quite busy and can be difficult to read, so I've used

There are two configurations to talk about in this section:
6.2.1 Using a low noise adapter to reduce the noise of the stock fans
As you can see in the above chart, two duty cycles were evaluated for the Foxconn fans: 35% and 50%. In terms of performance, it looks as though operating 2 Foxconn fans at 50% duty cycle would be sufficient to ensure ΔT < 25°C when the switch is under full load. However, this would be louder than the current Speed 1 configuration (35%), and so doesn't represent the kind of sound gains that I want to see.
6.2.2 Replacing the stock fans with another alternative
As it turns out, for just a direct replacement of the existing fans there is only one alternate fan that meets our requirement of ΔT < 25°C and that's the Mechatronics MR4020X12B1-RSR. At a total noise for 2 fans of 44 dBA, this represents a noise intensity 19x quieter than the stock fans. This solution is not without risk however, given the uncertainty associated with the system impedance curve. Looking at where it intersects the safety factor system impedance curve shows a ΔT ≈ 33°C, which is a bit warmer than I would like. If you're not feeling particularly rigid about the ΔT=25°C requirement and are willing to relax it slightly, the Mechatronics G4028H12B1-RSR has a slightly more forgiving P-Q curve. This fan has the same noise performance (44.0 dBA), but you can see that it intersects the safety factor system impedance curve at 24 CFM, which is much closer to the ΔT=30°C threshold.
Still, this safety factor performance for both fans isn't a show stopper - that's going to be a similar story for most of the fans in this assessment. I think either of these are a good solutions, but leaves some room for further noise optimisation as 44 dBA still isn't particularly quiet. Of the two, in this configuration, I would probably go for the Mechatronics G4028H12B1-RSR and sacrifice slight performance on the "typical" system impedance curve under the assumption that reality is slightly worse than this.
On reflection, a number of fan mod solutions proposed in these forums for the ICX7250-24P are represented in this chart, and it makes sense that people saw temperature issues. The Mechatronics 4020E12B1-RSR, Sunon MF40201VX-1000U-G99, and Delta EFB0412VHD-F00 generate between 13.7 and 15 CFM and are unable to meet the ΔT=50°C threshold. The Mechatronics MR4020M12B1-RSR, Comair Grphon GDA4028-12BB, Delta AFB0412HHB-F00 and the Delta FFB0412HN-F00 generate between 15.3 and 15.8 CFM in this configuration, and place them in the ΔT=45°C and ΔT=50°C temperature rise thresholds at best. These are amongst the quietest solutions of the alternatives, but none of these are acceptable solutions in this configuration without making other accommodations such as reducing the power load.
6.3 Three fans in parallel
With the addition of a third fan in parallel, a number of additional options are opened up to us as the airflow generation capability of the system is improved, as demonstrated below.

The following fans now meet our temperature threshold requirement of ΔT=25°C. These include the Same Sky CFM-4015B-1105-365-20 (41.3 dBA), Same Sky CFM-4020CF-195-342-20 (39.0 dBA), Delta AFFB0412VHB-F00 (41.3 dBA), Mechatronics MR4020H12B1-RSR (39.9 dBA), Mechatronics MH4028L12B1-RSR (43.8 dBA), Sanyo 109P0412B3013 (44.8 dBA), Mechatronics G4028M12B1-RSR (41.8 dBA), Sanyo 9L0412H301 (44.8 dBA), Mechatronics MR4020E12B1-RSR (43.9 dBA), Sanyo 109P0412G3013 (46.8 dBA), Wakefield DC0402812J2B-3T0 (42.8 dBA), Mechatronics MR4020X12B1-RSR (45.8 dBA), and the Mechantroics G4028H12B1-RSR (45.8 dBA).
The quietest of these are the Same Sky CFM-4020CF-195-342-20 (39.0 dBA) and the Mechatronics MR4020H12B1-RSR (39.9 dBA). Of the two, the Same Sky CFM-4020CF-195-342-20 intersects the safety factor impedance curve at 20 CFM, which corresponds to ΔT ≈ 37.5°C, whilst the Mechatronics MR4020H12B1-RSR intersects the safety factor system impedance curve at 21.2 CFM which corresponds to ΔT ≈ 36°C. I think that this temperature difference is probably marginal, and so in this case my preference would be the additional 0.9 dBA and the Same Sky fan. Having said that, if you are a bit less risk tolerant than I, then there a few more options further up the curve. For example, the Wakefield DC0402812J2B-3T0 (42.8 dBA) provides an impressive 38 CFM in the 3 fan configuration, which edges it across the ΔT=20°C threshold. Against the safety factor system impedance curve, it intersects at 26.9 CFM, corresponding to ΔT ≈ 28°C. This fan probably represents the least risky balance between performance and noise, however it is 3.8 dBA louder than the Same Sky alternative. There are of course quieter alternatives between these two, however the performance difference in the case of the safety factor system impedance curve is marginal; the Wakefield DC0402812J2B-3T0 is really the first that offers a substantial enough difference.
In comparison to the original Foxconn fans, three Same Sky CFM-4020CF-195-342-20 are 60x quieter, three Mechatronics MR4020H12B1-RSR are 49x quieter, and three Wakefield DC0402812J2B-3T0 are 26x quieter.
For those willing to run things a little hotter, or reduce the load on the switch for still-quieter alternatives, the Mechatronics MR4020M12B1-RSR (34.6 dBA) will run at 27 CFM for ΔT ≈ 27.5°C on the typical curve, and 18 CFM for ΔT ≈ 42.5°C on the safety factor curve. Quieter still is the Sunon MF40201VX-1000U-G99 (32.3 dBA) which will provide 26 CFM for ΔT ≈ 28°C on the typical curve, and 16.7 CFM for ΔT ≈ 45°C on the safety factor curve. You would really only want to consider these in a three fan configuration if you live in a location with a low ambient temperature, other active cooling solutions, or you intend to operate the switch at partial capacity.
6.4 Two fans in parallel, two fans in series
By adding two additional fans (four fans in total) in series with the original two, we see an improvement to static pressure, without an increase in maximum airflow. This doesn't do a great deal in the way of expanding the list of available options to us that meet the ΔT=25°C threshold, however what it does do is make all of the options more resilient; they have an increased ability to handle static pressure and are thus now able to maintain airflow to a much more similar capacity in systems that have more impedance.

In comparison to the 2 fans in parallel configuration, we now have both the Mechatronics MR4020X12B1-RSR (47.0 dBA) and the new addition of the Mechatronics G4028H12B1-RSR (47.0 dBA) that satisfy the ΔT=25°C threshold. The new addition is due to the increase in the slope of the curve due to the new static pressure resiliency of the fan system, which has increased the effective airflow the system is able to achieve under the system impedance. Additionally, due to the increased slope of the curve, the general trend here is that whilst there is a slight improvement in the airflow capability at the predicted typical 1U system impedance, the performance at the safety factor system impedance curve is substantially improved. This means that some fans that had good performance at the typical 1U system impedance curve but had high ΔT values at the safety factor impedance curve, now have much more reasonable performance at the safety factor impedance curve. To illustrate, the Mechatronics G4028H12B1-RSR produced an airflow of ≈24 CFM at the safety factor system impedance curve in the two fan configuration, corresponding to ΔT ≈ 31°C. In the 2+2 configuration, this same fan now generates ≈28 CFM, corresponding to ΔT ≈ 27.5°C, which is a shift across thresholds. Likewise, the Mechatronics MR4020H12B1-RSR (41.1 dBA) has transitioned from ΔT ≈ 42.5°C to ΔT ≈ 35°C. This improved resilience comes at the cost of additional noise, however.
Given that this configuration doesn't really change the calculus for fans at the typical 1U system impedance curve, my conclusion from this data is that going straight to this configuration would be cost inefficient. My suggestion would be to go for a parallel configuration first, and then if the realised system impedance deviates substantially from the modelling here, add additional fans first in parallel, and then in series. This will ensure that both cost and noise are kept to a minimum, and avoids the addition of unnecessary fans. The key takeaway from this though, is that in systems with high airflow impedance it is more valuable to add fans in series rather than in parallel (though both are valuable).
6.5 Three fans in parallel, three fans in series
Now we look at a 3+3 configuration (6 fans total). This broadly just exaggerates the effect we saw in the 2+2 configuration, however we can now see that we are much, much closer to the stock performance of 2x Foxconn fans.

This configuration provides a substantial boost to both airflow and static pressure performance. In this configuration, the Sunon MF40201VX-1000U-G99 (35.3 dBA) provides the quietest solution, representing a total solution 141x quieter than the original. This is followed by the Mechatronics MR4020M12B1-RSR (37.6 dBA), which represents a total solution 83x quieter than the original. In this configuration, the Sunon has slightly improved performance over the 3 parallel configuration, achieving a ΔT ≈ 25°C against the typical 1U system impedance curve. It performs much more reliably against the safety factor system impedance curve as well, at ΔT ≈ 32°C (improvement from ΔT ≈ 45°C). Note that this appears to be an identical fan to the Same Sky CFM-4020V-180-275-20 (35.3 dBA), which has an identical P-Q curve. It's worth noting also that there's still some cause for concern with performance against the safety factor system impedance. ΔT ≈ 32°C is quite close to the Speed 2 threshold, indicating that this cooling solution may not be sufficient to cool the solution sufficiently to return it to Speed 1. The Mechatronics MR4020M12B1-RSR performs slightly better than the Sunon/Same Sky, however it also adds 2.3 dBA to the noise; almost double the noise, and only has marginally better performance in the case where the safety factor system impedance is relevant.
Notable mentions here include the Com Air Gryphon GDA4028-12BB and the Delta FFB0412HN-F00; these improve the cooling performance tangibly for a typical 1U system, however fail to provide substantial additional tolerance to a system with higher static pressure as demonstrated by the safety factor system impedance curve, operating at ΔT ≈ 30°C. This may not be an issue, but selection of these depends on your risk tolerance and how accurately you think this analysis characterises the system impedance.
In order to develop confidence in the face of the uncertainty around system impedance, it seems as though the Same Sky CFM-4020CF-195-342-20 (42.0 dBA) offers the best solution, achieving ΔT ≈ 22.5°C in the typical 1U system impedance case, and ΔT ≈ 26°C in the safety factor impedance case. I wouldn't expect this to be silent at 42.0 dBA, however it does offer a substantial noise improvement over the Foxconn configuration (30x quieter).
7. Discussion and conclusion
To conclude, my broad thoughts of each of the possible solutions is:
For me, I need my lab to pass the wife test as it sits in my home office next to mine and my wife's desk. With that in mind, I'm open to a riskier solution where the fans may not meet the temperature targets outlined above for a fully loaded system. My mitigation to this risk is that I'm unlikely to load the switch with full PoE any time soon, and so I won't realise the error of my ways for quite a while. Therefore, my selection will be 3x Sunon MF40201VX-1000U-G99 initially. This will provide approx 26 CFM of airflow for a design temperature of ΔT ≈ 28°C. If the system impedance characterisation is too optimistic, I'm anticipating that the realised temperature rise could be as much as ΔT ≈ 45°C, which would be too hot to operate the switch at full capacity. In the case of this eventuality, I will either add more fans in serial to improve this performance (to an estimated ΔT ≈ 32°C at 24 CFM), replace the Sunon's with the Wakefield DC0402812J2B-3T0 (for an estimated ΔT ≈ 27°C), or add an additional fan to the ASIC as has been described in other successful fan mods.
For the ICX7250-48P, we're aiming for >60 CFM to stay within the ΔT=20°C - 25°C range. None of the fans I evaluated fall within this range. The closest was the Mechatronics G4028H12B2-RSR which with 3 fans in parallel generates 41.5 CFM at the typical 1U system impedance design point. If you were to use these fans, you would expect to see a temperature rise in the order of ΔT=35°C, which would likely push the switch into critical territory. Placing another 3 of these fans in series increases the total airflow to ~46 CFM, which improves things, but not enough to change things drastically. This still has a ΔT ≈ 32.5°C rise. Three of the Foxconn OEM fans in parallel only generate 68 CFM at the 1U typical impedance, so I'm hard pressed to imagine a quieter solution is available that satisfies the performance threshold, without adding more fans, larger fans (like the 120mm mods I've seen), or fans in different locations (like on top of the ASIC).
Having said that, as you can see there is a solution space to play around with if you don't need the maximum thermal capacity of the switch. If you're only using half the PoE load, then I suspect the comments about the ICX7250-24P will mostly apply.
As a final note, I hope that this has also made it obvious where there might be utility in going for very low noise, low CFM fans like the Noctua NF-A4x20. This type of fan has very low noise (14.9 dBA) and produces a maximum airflow of approx 5.5 CFM. As per the temperature thresholds chart above, ~5 CFM can cool up to 100W of heat generation with a temperature rise of ΔT=35°C. I would consider this the extreme outer range of performance, and would not trust this to an individual fan. In the interest of maintaining a temperature rise of ΔT=25°C, I would limit my usage of a single NF-A4x20 fan to applications less than 60W. This likely excludes many PoE switches. These fans also do not have a large static pressure rating, and Noctua haven't published any P-Q charts for them so it's difficult to know what the relationship looks like, but I would assume practically you will get less than 5 CFM of performance out of them in most applications. It's also worth noting that there are other reasons not to select these fans for the ICX7250-24P - there are minimum RPM thresholds that need to be satisfied so that the switch doesn't think that the fan has died; I've seen some reports that this has occurred with these fans.
Additionally, it's worth pointing out that another major deficiency in this analysis is the effective noise. All of this analysis has made assumptions based on the maximum sound pressure. Practically though, these fans are likely to be operating at some fractional speed, ideally at their most efficient around ~50%. Each of them will have unique noise profiles that may be better or worse, regardless of the maximum sound pressure value. They may have harmonics or whines that make them less tolerable, even if they are quieter. Unfortunately, the vendors didn't seem to publish much on this to draw insight from so in the absence of any personal experience this hasn't been treated as a decision point.
8. Selection and Recommendations
NOTE: Not all of the fans in these results have been tested. Use these at your own risk.
NOTE: You should come back to these recommendations after reading the Initial Results post, which highlights some issues with arranging fans in series.
I haven't implemented this design decision yet for the ICX7250-24P - I will edit this post with the results when they're available.
Initial results showing the outcomes of my purchases are available in the Initial Results post
Resources
Edit 15/05/2026: Update fan table to include confirmed and unconfirmed functionality in the switch
Edit 26/05/2026: Update selection and recommendations to (a) include a disclaimer about the recommendations being theoretical and unvalidated, and (b) resolve typo erroneously recommending the Sunon MF40101VX-1000U-G99 (10mm depth and not assessed) instead of the Sunon MF40201VX-1000U-G99 (20mm depth, assessed)
Edit 08/06/2026: Add links to initial results post
I've recently been through the process of trying to modify the fan configurations of a number of my servers from the stock OEM configuration to something else to reduce the amount of noise they produce. These servers were often designed without noise output as a meaningful consideration, and introducing that as a constraint has some trade-offs. My initial approach was to buy as many of the largest, highest CFM fans that I could, work out a way to mount them, and see if system temperatures stabilised with these new fans installed.
This approach left a lot of questions for me - what were the trade-offs that I'd made in this bargain? Was I still able to use these servers under full load without damaging the hardware? Had I selected the right hardware? Did I get enough fans to cover the thermal load? Were they placed geometrically in the right positions? Would these fans be satisfactory when I increase the number of hard drives in the server? In some cases, these fans weren't cheap either, and so exploring multiple solutions was becoming prohibitive.
So I decided to take a more engineering-based approach to better understand the design and solution space, so that I could make active decisions around some of these trade-offs. To be specific, the trade-offs that exist in this space when selecting a new fan are:
- Temperature load on the system (choosing a lower noise fan will place more heat load on the system)
- Fan noise (higher noise fans typically relieve heat load more effectively, but may not pass the wife test)
- Ability to load the system to its full performance (in the case of a switch, choosing to keep the heat load small and fan noise low may mean you can't use some/any ports for PoE, depending on where your chosen fan sits in the solution space)
This certainly isn't the only way to tackle this problem, but I thought others might get value from the process that I went through. If you enjoy over-engineering your homelab; this guide is for you!
Disclaimer: I have a background in physics and engineering but I'm not a HVAC engineer - I learnt a lot of this in the process of my exploration of the problem. There's every possibility I'm misinterpreting parts of the theory and how it should be used appropriately.
2. Concepts of air cooling performance analysis
There are two elements to air cooling performance as it relates to fan selection:
- The properties of the system, specifically how densely populated it is and the resulting system airflow impedance value (a pressure value, usually measured in Pa, in H2O or mm H2O)
- The properties of the fan, specifically the pressure-airflow (P-Q) curve - how much airflow (usually measured in CFM or m^3/min) can the fan induce at different static pressure levels
In a free stream of air, there is no system impedance. This is where the Max Airflow measurements are taken, and is often what's reported in performance summaries. That means that the maximum airflow metric may be a relevant to you if you're intending your cooling solution to operate in a largely sparse/unpopulated environment (think single CPU 4U/5U or ATX form factor systems, though it always depends on the specific system). If the system is densely populated on the other hand (think 1U and 2U servers, particularly if they have a lot of hot-swap HDD bays), this metric is likely less valuable. What you're interested in is the airflow (CFM) that can be achieved at the system impedance, and so inspection of a P-Q chart is imperative.
System impedance is made up of two elements:
- The static pressure of the system
- The dynamic pressure resulting from the flow of air
On a fan specification summary data sheet, the "maximum static pressure" is also often cited, which is the system impedance (static pressure) at which the fan is unable to induce a flow of air (CFM=0). It is not possible for a fan to achieve its maximum airflow (CFM), and it's maximum static pressure at the same time. The airflow that a fan is capable of producing is determined by the static pressure of the system, and so performance of a fan is definitionally dependent on the system it is being used in and the role it is playing within that system (is it a case fan, a CPU fan attached to a heat-sink, a radiator fan?).
This is made a bit clearer by looking at the difference between placing two fans in parallel or in series (discussed later).
Note: I'm pretty inconsistent with units in this write-up. I have a strong preference for using SI wherever I can, but the resources and data around this are a bit of a mess. I've used SI wherever possible, except in the representation of performance where I've stuck to CFM and in H2O. Note that for the calculations to work you can't mix and match unit systems. For reliable results make sure you're only ever using SI when calculating quantities.
2.1 A note on determining system impedance
Having some kind of estimation of system impedance is critical to performing analysis this way. Without it, it's impossible to know where on the P-Q curve the system is and you have no basis for decision making. In order to get an estimate, the gold standard here would be to do this experimentally and take measurements of the system using a pitot tube and a manometer to properly characterise it. More generally though (in the absence of an ability to fully derive this experimentally), the system impedance follows the "square law", characterised by this equation:
P = KρQⁿ
where:
- P : Static pressure (in H2O)
- K : The load factor
- ρ : The density of the fluid (lb/ft^3)
- Q : The flow rate (CFM)
- n : A constant, where n=2 approximates a turbulent system. n=1 characterises laminar flow, which is not the case here.
Given a system characteristic coordinate (P, Q) (from someone else's effort to characterise a similar system experimentally), we can solve this equation for K and then build up a system impedance curve. To illustrate:
K = P / ρQⁿ
Once we have K, we can substitute it back into the original equation for a sweep of Q values and plot the resulting P values. The utility of this relies on obtaining data from elsewhere, but this will be shown on graphs later using the limited information I was able to find.
2.2 How does placing fans in series or parallel affect cooling performance?
The general principle is discussed in the following sections.
2.2.1 Two fans in parallel
When two fans are placed in parallel, this primarily improves the airflow of the system. However, when compared to a single fan, it also sees a small improvement to static pressure performance, as demonstrated below:

As you can see, the system impedance curve intersects the parallel fan performance curve at both a higher static pressure, and it also produces a higher airflow. However, the intent of this configuration is to increase airflow in low static pressure systems, and the effect of this in the example above would have been more effective if the system impedance curve was lower.
2.2.2 Two fans in series
In contrast, when two fans are placed in series, this improves the ability for a fan system to operate with high system impedance. Like in parallel, we see an increase to both static pressure performance and airflow performance, however biased towards static pressure:

As can be seen, the system impedance curve intersects the fan system in series at both a higher static pressure and a higher airflow.
Both the concepts of parallel and series arrangements will be explored in the solution space later on to support selection.
3. Characterising the system
Before making changes to the system, it's good to understand how it currently performs, at least as the basis for evaluating alternatives, but also to better understand the designed-for performance regime.
The Brocade ICX7250-24P contains two Foxconn PIA040H12P 40x40x28mm exhaust fans arranged in parallel, each of which has a maximum air flow rating of 26.33 CFM and a maximum static pressure rating of 2.04 in H₂O.
In terms of the system impedance, I was unable to find any information specific to the Brocade ICX7250-24P, or any other Brocade product for that matter. This is considered a major limitation of this analysis. In fact, it was shockingly difficult to find any values for 1U servers more generally with any basis in reality. However, I did manage to find some for 1U and 2U servers that were produced by IBM and published in "Analysis of Airflow Distribution Across a Front-to-Rear Server Rack" (Radmehr et al., 2007):
| Server | Airflow (CFM) | Static Pressure (in H₂O) |
|---|---|---|
| 1U | 43 | 0.15 |
| 2U | 155 | 0.54 |
There are a few limitations associated with using these values. A non-exhaustive list includes:
- They apply to high end IBM servers, not Brocade switches
- They apply to servers, and not switches. Switches often lack the depth of servers, and have quite a different distribution of internal componentry (i.e., switches don't contain hard drives or large heat sinks).
This current system performance is summarised in the following P-Q chart (fan characteristics digitised from data sheets):

Note that the single fan performance is only shown here for informational purposes. The total system fan performance is represented by the orange line. As can be seen, at the system fan curve intersects with the system impedance curve at (Q=49.3 CFM, P=0.2 in H₂O). Since these fan performance curves indicate airflow potential when operated at 12V (100% duty cycle), this means that the system designers anticipated that 49.3 CFM would be sufficient to keep the system within acceptable thermal thresholds when operating it at maximum load.
At idle, in Speed 1 (not the full speed shown above delivering 49.3 CFM), the system has the following measurements:
Code:
SSH@icx7250-24p-router>show chassis
The stack unit 1 chassis info:
Power supply 1 (AC - PoE) present, status ok
Power supply 2 not present
Fan 1 ok, speed (auto): [[1]]<->2
Fan 2 ok, speed (auto): [[1]]<->2
Fan controlled temperature:
Rule 1/2 (MGMT THERMAL PLANE): 60.0 deg-C
Rule 2/2 (AIR OUTLET NEAR PSU): 33.5 deg-C
Fan speed switching temperature thresholds:
Rule 1/2 (MGMT THERMAL PLANE):
Speed 1: NM<-----> 93 deg-C
Speed 2: 82<----->105 deg-C (shutdown)
Rule 2/2 (AIR OUTLET NEAR PSU):
Speed 1: NM<-----> 58 deg-C
Speed 2: 49<----->105 deg-C (shutdown)
Fan 1 Air Flow Direction: Front to Back
Fan 2 Air Flow Direction: Front to Back
Slot 1 Current Temperature: 60.7 deg-C (Sensor 1), 33.0 deg-C (Sensor 2)
Slot 2 Current Temperature: NA
Warning level.......: 100.0 deg-C
Shutdown level......: 105.0 deg-C
Code:
SSH@icx7250-24p-router#dm fan
Fan 1 Speed at 6279 RPM.
Fan 2 Speed at 6398 RPM.
4. Understanding the thermal requirements
Before we get stuck into analysing different fans, it's useful to have a meaningful lens through which to view that performance. Namely, how much airflow do I actually need to cool my system? Armed with that information, we'll be able to identify the alternatives that are "good enough". Fortunately, the amount of heat produced by electronic components matches closely with the power consumed by the system, so we can derive the airflow requirements using the system power consumption.
4.1 Power Load
First, let's understand the requirement. We can look at the power consumption figures provided in the technical specifications for the Brocade ICX7250 series of switches, which provide the following consumption values for a few performance regimes (I assume 200VAC input here):
| Configuration | ICX7250-24P (W) | ICX7250-48P (W) |
|---|---|---|
| Idle | 48 | 70.8 |
| Typical | 428 | 862 |
| Maximum | 439 | 880 |
Note that the "Typical" configuration assumes that all ports have a PoE load and 10% traffic. The difference between this and the "Maximum" configuration is that the Maximum configuration has 100% traffic. In this case, PoE is obviously the biggest consumer of power.
Note: I've only included the PoE variants of the switches here because they are the most interesting. If you have a non-PoE variant, you should be able to follow the same process but your requirements will be far less constrained, so your performance will be impacted less by your fan selection.
4.2 Required airflow calculation methodology
The sensible heat equation gives us a model for understanding the trade-offs between power consumption, designed temperature rise and required airflow:
hₛ = cₚρQΔT
where:
- hₛ : sensible heat (W). This is often also represented as BTU/hr in imperial.
- cₚ : specific heat of air (assumed constant standard atmosphere 1006 J/kgC - this assumption could probably be improved as cₚ varies with temperature)
- ρ : density of the air (1.202 kg/m^3 standard atmosphere)
- Q : airflow (m^3/s - we'll use this to find the representation in CFM later)
- ΔT : temperature rise from the inlet (°C)
This can be used a couple of ways:
1. to find out what airflow requirements we have to meet a temperature goal:
Q = hₛ / cₚρΔT
2. to understand what temperature impact using specific fans with specific airflow performance have
ΔT = hₛ / cₚρQ
4.3 Results
I've performed a sweep of parameters Q, hₛ and ΔT in the above equation to make the relationships a bit easier to visualise. The figure below shows how the airflow requirements vary for different heat loads, with different design temperature rises. I've also shown where the power load for the ICX7250-24P and ICX7250-48P lie on this chart. To read this, look at the CFM associated with the intersection point of these power loads and the desired temperature differential.

There are a few interesting insights to pull out of this:
- As per above, the design airflow for the ICX7250-24P is 49.3 CFM. Looking at the intersection of the ICX7250-24P "Maximum" line with ~50 CFM, we can see that this corresponds to a design temperature rise of ~15°C. However, since the ICX7250-24P shares a lot of design commonality with the ICX7250-48P, it's possible that the design goals of these switches are not independent. For validation, I also generated the system characteristics for the IXC7250-48P (which includes a third Foxconn fan in parallel). This showed that the ICX7250-48P cooling system generates ~68 CFM, which intersects with the "ICX7250-48P Maximum" line between 20°C and 25°C - lets assume that this is approx 22.5°C. I suspect that this is actually the true thermal design range, and they just removed a fan in the ICX7250-24P since 2 fans still exceeded the designed-for thermal performance, but 1 fan would not have.
- As little as 3.3 CFM can support the thermal load of the ICX7250-24P at idle for a ΔT=25°C target (note that this assumes no traffic)
- As little as 5 CFM can support the thermal load of the ICX7250-48P at idle for a ΔT=25°C target (note that this assumes no traffic)
- Interestingly, for the ICX7250-24P, small gains in CFM at the Maximum threshold seem to have a large impact on the cooling performance of the system. The span between ΔT=50°C (15 CFM) and ΔT=35°C (22 CFM) is only 7 CFM. Likewise, the span between ΔT=20°C (~38 CFM) and ΔT=35°C (~22 CFM) is only ~16 CFM. This indicates that at the lower end, small changes are likely to make a large difference. This also complicates things for us from a selection perspective, because our uncertainty in system performance will reduce our confidence that we can accurately identify whether the temperature differential is ΔT=35°C or ΔT=50°C.
- Unfortunately, I'm missing information about the relationship between fan RPM and CFM for most of the fans under assessment, including the OEM Foxconn fan, so it's not perfectly clear what conditions led to my initial measurement of 60 degrees at idle. For the purposes of this, I'll assume:
- Speed 1 corresponds to a 35% duty cycle
- 35% duty cycle generates 35% the total airflow = ~18 CFM, which means 60°C is approx a 5°C temperature differential.
- Therefore, a 35 degree rise corresponds to approx 55°C+ 35°C= 90°C
- Of course, this will depend on ambient temperatures in your locations. The 55°C here represents ambient temperature + heat transfer from adjacent server elements in the rack
- Given observations (4) and (5), it seems to me that the desirable temperature range to opt for is between 20°C and 25°C, which appears to align with the Brocade design engineers perspective too. You could probably extend this to 30°C if you're running short on options, however this is pushing very close to the critical threshold of 93°C at which point the ICX7250-24P ramps up into Speed 2 (100%), which will not serve us well to reduce noise. There's a concern here as well in that if Speed 2 is not able to reduce the temperature back down sufficiently low, the switch will never revert back to Speed 1, so it is in your interest from a sound perspective to choose a fan with enough performance headroom to do this. There is also more uncertainty about performance in this selection region.
To summarise:
| Design ΔT (°C) | ICX7250-24P Airflow Requirement (CFM) | ICX7250-48P Airflow Requirement (CFM) |
|---|---|---|
| 20 | 38 | 76 |
| 25 | 30 | 60 |
| 30 | 25 | 50 |
To state the obvious, the other dimension that hasn't been discussed here is operating the switch in a manner that doesn't take it to its design load. Managing the amount of energy consumed is another way to bring down the airflow requirements without sacrificing the design temperature. To plan your cooling solution around some fractional capacity, simply take the intended power consumption and identify the airflow requirements at the ΔT of your choice. In this case, an easy win for users of the ICX7250-48P would be to adopt a policy of using some fraction of the total PoE ports. To illustrate, if you chose to only use 24 of your 48 ports with PoE, your requirements would relax to something approximating the ICX7250-24P.
5. Fan performance
Below are a selection of fans for comparison. These fans are a mix of:
- Fans that have been recommended as good candidates for substitution in Brocade ICX Series (cheap & powerful 10gbE/40gbE switching)
- Fans that have been recommended by YouTubers and eBay vendors
- Fans identified as within the desired performance regime (noise, airflow) from a search on Digikey
| Ref | Model | Availability | Max Airflow (CFM) | Max Pressure (inH2O) | Max Sound Level (dBA) | Estimated noise (2 fans, dBA) | Estimated noise (3 fans, dBA) | Relative noise intensity (3 fans) wrt. 2x Foxconn fans | Comment | Status |
|---|---|---|---|---|---|---|---|---|---|---|
| 1 | Foxconn PIA040H12P-F02-AB | Aliexpress | 26.33 | 2.04 | 53.8 | 56.8 | 59 | 1.7x louder | Stock OEM selection | Tested OK |
| 2 | Sunon MF40201VX-1000U-G99 | Digikey | 10.8 | 0.29 | 27.5 | 30.5 | 32.3 | 282x quieter | Tested OK | |
| 3 | Same Sky CFM-4020V-180-275-20 | Digikey | 10.8 | 0.29 | 27.5 | 30.5 | 32.3 | 282x quieter | Identical P-Q curve to Sunon MF40201VX-1000U-G99 | Tested OK |
| 4 | Mechatronics MR4020M12B1-RSR | Digikey (bulk only) Bravo Electro | 11.5 | 0.24 | 29.8 | 32.8 | 34.6 | 166x quieter | Untested | |
| 5 | Comair Rotron Gryphon GDA4028-12BB | ?? | 11.26 | 0.34 | 31.44 | 34.45 | 36.2 | 115x quieter | "Unobtainium", but here for comparison | Reported OK |
| 6 | Mechatronics G4020E12B1-RSR | Digikey (bulk only) Bravo Electro | 11.7 | 0.23 | 32 | 35 | 36.8 | 100x quieter | Untested | |
| 7 | Delta AFB0412HHB-F00 | Digikey (bulk only) | 11.5 | 0.359 | 32 | 35 | 36.8 | 100x quieter | Untested | |
| 8 | Delta FFB0412HN-F00 | Digikey | 10.6 | 0.248 | 32.1 | 35.1 | 36.9 | 98x quieter | Reported OK | |
| 9 | Delta EFB0412VHD-F00 | Digikey | 10.1 | 0.416 | 32.5 | 35.5 | 37.2 | 91x quieter | Reported OK | |
| 10 | Same Sky CFM-4020CF-195-342-20 | Digikey Mouser | 11.9 | 0.41 | 34.2 | 37.2 | 39 | 60x quieter | Untested | |
| 11 | Mechatronics MR4020H12B1-RSR | Digikey (bulk only) Bravo Electro | 13.6 | 0.34 | 35.1 | 38.1 | 39.9 | 49x quieter | Untested | |
| 12 | Delta AFFB0412VHB-F00 | Digikey (bulk only) | 13 | 0.459 | 36.5 | 39.5 | 41.3 | 35x quieter | Untested | |
| 13 | Same Sky CFM-4015B-1105-365-20 | Digikey | 12.3 | 0.56 | 36.5 | 39.5 | 41.3 | 35x quieter | Untested | |
| 14 | Sanyo Denki 109P0412H3013 | Digikey | 11.3 | 0.414 | 37 | 40 | 41.7 | 32x quieter | Untested | |
| 15 | Mechatronics G4028M12B1-RSR | Digikey (bulk only) | 13 | 0.37 | 37 | 40 | 41.8 | 32x quieter | Untested | |
| 16 | Wakefield DC0402812J2B-3T0 | Digikey | 13.8 | 0.46 | 38 | 41 | 42.7 | 26x quieter | Reported fan failure in Speed 1 | |
| 17 | Mechatronics MH4028L12B1-RSR | ?? | 12.8 | 0.33 | 39 | 42.01 | 43.8 | 20x quieter | Untested | |
| 18 | Mechatronics MR4020E12B1-RSR | Digikey (bulk only) | 15.8 | 0.45 | 39.1 | 42.1 | 43.9 | 19x quieter | Untested | |
| 19 | Sanyo Denki 109P0412B3013 | Digikey | 13.4 | 0.574 | 40 | 43 | 44.7 | 16x quieter | Reported OK | |
| 20 | Sanyo Denki 9L0412H301 | Digikey | 13.1 | 0.426 | 40 | 43 | 44.7 | 16x quieter | Untested | |
| 21 | Mechatronics MR4020X12B1-RSR | Digikey | 17.3 | 0.54 | 41 | 44 | 45.7 | 13x quieter | Reported OK | |
| 22 | Mechatronics G4028H12B1-RSR | Digikey (bulk only) | 16 | 0.57 | 41 | 44 | 45.7 | 13x quieter | Untested | |
| 23 | Sanyo Denki 109P0412G3013 | Digikey | 14.8 | 0.719 | 42 | 45 | 46.7 | 10x quieter | Reported OK |
In order to get a better view of how each of the candidate fans performed relative to each other, I digitised all of the performance charts that the vendors provide (shout out to Engauge Digitizer), and overlayed this with the system impedance curves described earlier to help guide our assessment of the performance regime of these fans that we should care about.

Note: Like-for-like performance should be compared at the points at which each fan intersects the "Typical 1U system impedance" curve, which follows a square law. You should not just compare values at the same static pressure; these are not comparable due to the dynamic pressure component of system impedance produced by the airflow itself.
We shouldn't read too much into this figure; these represent the single fan performance, and what we really care about is the total system performance. Having said that, it's exceedingly obvious just how much better the OEM Foxconn fans are than any of the other alternatives being evaluated, both from a pressure and airflow perspective. It's also surprising how the performance regime demonstrated by the "typical 1U system impedance" curve is so close to the maximal airflow performance of the fans. If this assessment of the system impedance is realistic, then the first order analysis described in the introduction is probably sufficient; comparing the max CFM values (and ignoring static pressure as a metric) is probably "close enough". Additionally, looking at the chart, the distance between the OEM fan and the next most performant stays roughly equidistant for the entirety of the profile.
As mentioned earlier, the default configuration for the ICX7250-24P is two exhaust fans arranged in parallel at the rear of the chassis. This is the baseline from which performance will be compared. In the case of the ICX7250-24P, there is an unused mounting point for a third fan, and usage of this should form part of the solution space. The following configurations will be assessed in the following section:
- Removing one of the existing OEM Foxconn fans and operating the switch with a single fan to reduce noise
- Applying a low noise adapter to reduce the duty cycle of the existing OEM Foxconn fans to reduce noise
- Replacing the two existing OEM Foxconn fans with an alternate and keeping them in a parallel configuration
- Replacing the existing two and adding a third fan in parallel
- Replacing the existing two and adding an additional two fans in series (4 fans total)
- Replacing the existing two, adding a third, and adding an additional three fans in series (6 fans total)
6.1 Single Foxconn fan
As can be seen in the single fan performance chart above, the usage of a single Foxconn fan would generate ≈26 CFM at the system impedance. This is a viable alternative, generating a ΔT ≈ 30°C at the maximum load of the ICX7250-24P, if a little hotter than I would prefer. This is also effective at reducing the sound output by (2 times quieter) at maximum load. However, another consideration is the noise when not loaded up to the maximum load. At Speed 1, these fans operate at 35% duty cycle. This generates 9 CFM from one fan, which is enough to support 128W of heat at ΔT = 25°C or 156W at ΔT = 30°C. I don't have any data to quantify the noise level at this duty cycle (I haven't been able to find noise/RPM curves for any of the fans assessed), but in my personal anecdotal experience it is too loud, and offers limited improvement over just keeping the stock configuration.
The following are the measurements I took after letting the switch reach a steady state with only a single fan:
Code:
SSH@icx7250-24p-router>show chassis
The stack unit 1 chassis info:
Power supply 1 (AC - PoE) present, status ok
Power supply 2 not present
Fan 1 ok, speed (auto): [[1]]<->2
Fan 2 failed
Fan controlled temperature:
Rule 1/2 (MGMT THERMAL PLANE): 74.5 deg-C
Rule 2/2 (AIR OUTLET NEAR PSU): 39.5 deg-C
Fan speed switching temperature thresholds:
Rule 1/2 (MGMT THERMAL PLANE):
Speed 1: NM<-----> 93 deg-C
Speed 2: 82<----->105 deg-C (shutdown)
Rule 2/2 (AIR OUTLET NEAR PSU):
Speed 1: NM<-----> 58 deg-C
Speed 2: 49<----->105 deg-C (shutdown)
Fan 1 Air Flow Direction: Front to Back
Fan 2 Air Flow Direction: Front to Back
Slot 1 Current Temperature: 74.5 deg-C (Sensor 1), 39.5 deg-C (Sensor 2)
Slot 2 Current Temperature: NA
Warning level.......: 100.0 deg-C
Shutdown level......: 105.0 deg-C
Code:
SSH@icx7250-24p-router#dm fan
Fan 1 Speed at 6282 RPM.
Fan 2 Speed at 182 RPM.
6.2 Two fans in parallel
As a reminder, the way to read the performance on the following chart is to identify the airflow generated at the intersection point of each fans curve and the relevant system impedance curve. I have also marked where the predicted temperature rise thresholds exist for the full load configuration of the ICX7250-24P. These thresholds will be different for the ICX7250-48P. In order to identify which fans meet the ΔT=25°C threshold, look at the fan performance curves that intersect the system impedance curve to the right of this threshold.
The legend in these charts shows each fan model in a unique colour. I appreciate these charts are quite busy and can be difficult to read, so I've used
distinctipy to make these colours as distinguishable from each other as possible (if not pretty, make it functional). I've also shown the predicted noise for the entire solution in the legend entry (i.e., noise for 2 fans in this case, more in the subsequent configurations).
There are two configurations to talk about in this section:
6.2.1 Using a low noise adapter to reduce the noise of the stock fans
As you can see in the above chart, two duty cycles were evaluated for the Foxconn fans: 35% and 50%. In terms of performance, it looks as though operating 2 Foxconn fans at 50% duty cycle would be sufficient to ensure ΔT < 25°C when the switch is under full load. However, this would be louder than the current Speed 1 configuration (35%), and so doesn't represent the kind of sound gains that I want to see.
6.2.2 Replacing the stock fans with another alternative
As it turns out, for just a direct replacement of the existing fans there is only one alternate fan that meets our requirement of ΔT < 25°C and that's the Mechatronics MR4020X12B1-RSR. At a total noise for 2 fans of 44 dBA, this represents a noise intensity 19x quieter than the stock fans. This solution is not without risk however, given the uncertainty associated with the system impedance curve. Looking at where it intersects the safety factor system impedance curve shows a ΔT ≈ 33°C, which is a bit warmer than I would like. If you're not feeling particularly rigid about the ΔT=25°C requirement and are willing to relax it slightly, the Mechatronics G4028H12B1-RSR has a slightly more forgiving P-Q curve. This fan has the same noise performance (44.0 dBA), but you can see that it intersects the safety factor system impedance curve at 24 CFM, which is much closer to the ΔT=30°C threshold.
Still, this safety factor performance for both fans isn't a show stopper - that's going to be a similar story for most of the fans in this assessment. I think either of these are a good solutions, but leaves some room for further noise optimisation as 44 dBA still isn't particularly quiet. Of the two, in this configuration, I would probably go for the Mechatronics G4028H12B1-RSR and sacrifice slight performance on the "typical" system impedance curve under the assumption that reality is slightly worse than this.
On reflection, a number of fan mod solutions proposed in these forums for the ICX7250-24P are represented in this chart, and it makes sense that people saw temperature issues. The Mechatronics 4020E12B1-RSR, Sunon MF40201VX-1000U-G99, and Delta EFB0412VHD-F00 generate between 13.7 and 15 CFM and are unable to meet the ΔT=50°C threshold. The Mechatronics MR4020M12B1-RSR, Comair Grphon GDA4028-12BB, Delta AFB0412HHB-F00 and the Delta FFB0412HN-F00 generate between 15.3 and 15.8 CFM in this configuration, and place them in the ΔT=45°C and ΔT=50°C temperature rise thresholds at best. These are amongst the quietest solutions of the alternatives, but none of these are acceptable solutions in this configuration without making other accommodations such as reducing the power load.
6.3 Three fans in parallel
With the addition of a third fan in parallel, a number of additional options are opened up to us as the airflow generation capability of the system is improved, as demonstrated below.

The following fans now meet our temperature threshold requirement of ΔT=25°C. These include the Same Sky CFM-4015B-1105-365-20 (41.3 dBA), Same Sky CFM-4020CF-195-342-20 (39.0 dBA), Delta AFFB0412VHB-F00 (41.3 dBA), Mechatronics MR4020H12B1-RSR (39.9 dBA), Mechatronics MH4028L12B1-RSR (43.8 dBA), Sanyo 109P0412B3013 (44.8 dBA), Mechatronics G4028M12B1-RSR (41.8 dBA), Sanyo 9L0412H301 (44.8 dBA), Mechatronics MR4020E12B1-RSR (43.9 dBA), Sanyo 109P0412G3013 (46.8 dBA), Wakefield DC0402812J2B-3T0 (42.8 dBA), Mechatronics MR4020X12B1-RSR (45.8 dBA), and the Mechantroics G4028H12B1-RSR (45.8 dBA).
The quietest of these are the Same Sky CFM-4020CF-195-342-20 (39.0 dBA) and the Mechatronics MR4020H12B1-RSR (39.9 dBA). Of the two, the Same Sky CFM-4020CF-195-342-20 intersects the safety factor impedance curve at 20 CFM, which corresponds to ΔT ≈ 37.5°C, whilst the Mechatronics MR4020H12B1-RSR intersects the safety factor system impedance curve at 21.2 CFM which corresponds to ΔT ≈ 36°C. I think that this temperature difference is probably marginal, and so in this case my preference would be the additional 0.9 dBA and the Same Sky fan. Having said that, if you are a bit less risk tolerant than I, then there a few more options further up the curve. For example, the Wakefield DC0402812J2B-3T0 (42.8 dBA) provides an impressive 38 CFM in the 3 fan configuration, which edges it across the ΔT=20°C threshold. Against the safety factor system impedance curve, it intersects at 26.9 CFM, corresponding to ΔT ≈ 28°C. This fan probably represents the least risky balance between performance and noise, however it is 3.8 dBA louder than the Same Sky alternative. There are of course quieter alternatives between these two, however the performance difference in the case of the safety factor system impedance curve is marginal; the Wakefield DC0402812J2B-3T0 is really the first that offers a substantial enough difference.
In comparison to the original Foxconn fans, three Same Sky CFM-4020CF-195-342-20 are 60x quieter, three Mechatronics MR4020H12B1-RSR are 49x quieter, and three Wakefield DC0402812J2B-3T0 are 26x quieter.
For those willing to run things a little hotter, or reduce the load on the switch for still-quieter alternatives, the Mechatronics MR4020M12B1-RSR (34.6 dBA) will run at 27 CFM for ΔT ≈ 27.5°C on the typical curve, and 18 CFM for ΔT ≈ 42.5°C on the safety factor curve. Quieter still is the Sunon MF40201VX-1000U-G99 (32.3 dBA) which will provide 26 CFM for ΔT ≈ 28°C on the typical curve, and 16.7 CFM for ΔT ≈ 45°C on the safety factor curve. You would really only want to consider these in a three fan configuration if you live in a location with a low ambient temperature, other active cooling solutions, or you intend to operate the switch at partial capacity.
6.4 Two fans in parallel, two fans in series
By adding two additional fans (four fans in total) in series with the original two, we see an improvement to static pressure, without an increase in maximum airflow. This doesn't do a great deal in the way of expanding the list of available options to us that meet the ΔT=25°C threshold, however what it does do is make all of the options more resilient; they have an increased ability to handle static pressure and are thus now able to maintain airflow to a much more similar capacity in systems that have more impedance.

In comparison to the 2 fans in parallel configuration, we now have both the Mechatronics MR4020X12B1-RSR (47.0 dBA) and the new addition of the Mechatronics G4028H12B1-RSR (47.0 dBA) that satisfy the ΔT=25°C threshold. The new addition is due to the increase in the slope of the curve due to the new static pressure resiliency of the fan system, which has increased the effective airflow the system is able to achieve under the system impedance. Additionally, due to the increased slope of the curve, the general trend here is that whilst there is a slight improvement in the airflow capability at the predicted typical 1U system impedance, the performance at the safety factor system impedance curve is substantially improved. This means that some fans that had good performance at the typical 1U system impedance curve but had high ΔT values at the safety factor impedance curve, now have much more reasonable performance at the safety factor impedance curve. To illustrate, the Mechatronics G4028H12B1-RSR produced an airflow of ≈24 CFM at the safety factor system impedance curve in the two fan configuration, corresponding to ΔT ≈ 31°C. In the 2+2 configuration, this same fan now generates ≈28 CFM, corresponding to ΔT ≈ 27.5°C, which is a shift across thresholds. Likewise, the Mechatronics MR4020H12B1-RSR (41.1 dBA) has transitioned from ΔT ≈ 42.5°C to ΔT ≈ 35°C. This improved resilience comes at the cost of additional noise, however.
Given that this configuration doesn't really change the calculus for fans at the typical 1U system impedance curve, my conclusion from this data is that going straight to this configuration would be cost inefficient. My suggestion would be to go for a parallel configuration first, and then if the realised system impedance deviates substantially from the modelling here, add additional fans first in parallel, and then in series. This will ensure that both cost and noise are kept to a minimum, and avoids the addition of unnecessary fans. The key takeaway from this though, is that in systems with high airflow impedance it is more valuable to add fans in series rather than in parallel (though both are valuable).
6.5 Three fans in parallel, three fans in series
Now we look at a 3+3 configuration (6 fans total). This broadly just exaggerates the effect we saw in the 2+2 configuration, however we can now see that we are much, much closer to the stock performance of 2x Foxconn fans.

This configuration provides a substantial boost to both airflow and static pressure performance. In this configuration, the Sunon MF40201VX-1000U-G99 (35.3 dBA) provides the quietest solution, representing a total solution 141x quieter than the original. This is followed by the Mechatronics MR4020M12B1-RSR (37.6 dBA), which represents a total solution 83x quieter than the original. In this configuration, the Sunon has slightly improved performance over the 3 parallel configuration, achieving a ΔT ≈ 25°C against the typical 1U system impedance curve. It performs much more reliably against the safety factor system impedance curve as well, at ΔT ≈ 32°C (improvement from ΔT ≈ 45°C). Note that this appears to be an identical fan to the Same Sky CFM-4020V-180-275-20 (35.3 dBA), which has an identical P-Q curve. It's worth noting also that there's still some cause for concern with performance against the safety factor system impedance. ΔT ≈ 32°C is quite close to the Speed 2 threshold, indicating that this cooling solution may not be sufficient to cool the solution sufficiently to return it to Speed 1. The Mechatronics MR4020M12B1-RSR performs slightly better than the Sunon/Same Sky, however it also adds 2.3 dBA to the noise; almost double the noise, and only has marginally better performance in the case where the safety factor system impedance is relevant.
Notable mentions here include the Com Air Gryphon GDA4028-12BB and the Delta FFB0412HN-F00; these improve the cooling performance tangibly for a typical 1U system, however fail to provide substantial additional tolerance to a system with higher static pressure as demonstrated by the safety factor system impedance curve, operating at ΔT ≈ 30°C. This may not be an issue, but selection of these depends on your risk tolerance and how accurately you think this analysis characterises the system impedance.
In order to develop confidence in the face of the uncertainty around system impedance, it seems as though the Same Sky CFM-4020CF-195-342-20 (42.0 dBA) offers the best solution, achieving ΔT ≈ 22.5°C in the typical 1U system impedance case, and ΔT ≈ 26°C in the safety factor impedance case. I wouldn't expect this to be silent at 42.0 dBA, however it does offer a substantial noise improvement over the Foxconn configuration (30x quieter).
7. Discussion and conclusion
To conclude, my broad thoughts of each of the possible solutions is:
- Removing one of the existing OEM Foxconn fans and operating the switch with a single fan to reduce noise
- Whilst seemingly effective, performance wise, it doesn't appreciably reduce the noise, so not a viable solution
- Applying a low noise adaptor to reduce the duty cycle of the existing OEM Foxconn fans to reduce noise
- As with (1), the fans are too noisy even at low RPMs for this to be considered an effective treatment
- Replacing the two existing OEM Foxconn fans with an alternate and keeping them in a parallel configuration
- One solution stood out in this space; the Mechatronics MR4020X12B1-RSR which satisfied the design temperature threshold, however did so at 44 dB. There are quieter solutions in the remaining options, so this shouldn't be considered.
- Replacing the existing two and adding a third fan in parallel
- A reasonably large number of fans stood out in this space. The Same Sky CFM-4020CF-195-342-20 (39 dBA) and the Mechatronics MR4020H12B1-RSR (39.9 dBA) performed similarly and yielded the quietest results, however suffer from poor performance in environments with higher static pressure, leading to a risk of overheating if the "Typical 1U system impedance curve" has been too poorly estimated.
- Replacing the existing two and adding an additional two fans in series (4 fans total)
- Only two fans met our design requirements in this configuration; the Mechatronics MR4020X12B1-RSR (47.0 dBA) and the Mechatronics G4028H12B1-RSR (47.0 dBA), however I don't consider this an actionable solution given how non-competitive 47 dBA is in comparison to other solutions.
- Replacing the existing two, adding a third, and adding an additional three fans in series (6 fans total)
- Surprisingly, this solution turned out to be the one that yielded the most resilient and quietest solution. The candidate solutions resulting from this are:
- 6x Sunon MF40201VX-1000U-G99 (total 35.3 dBA) or 6x Same Sky CFM-4020V-180-275-20 (total 35.3 dBA) for the quietest solution
- 6x Mechatronics MR4020M12B1-RSR (37.6 dBA)
- 6x Same Sky CFM-4020CF-195-342-20 (42.0 dBA), which offers the best performance guarantees with the cost of poorer noise performance
- Surprisingly, this solution turned out to be the one that yielded the most resilient and quietest solution. The candidate solutions resulting from this are:
For me, I need my lab to pass the wife test as it sits in my home office next to mine and my wife's desk. With that in mind, I'm open to a riskier solution where the fans may not meet the temperature targets outlined above for a fully loaded system. My mitigation to this risk is that I'm unlikely to load the switch with full PoE any time soon, and so I won't realise the error of my ways for quite a while. Therefore, my selection will be 3x Sunon MF40201VX-1000U-G99 initially. This will provide approx 26 CFM of airflow for a design temperature of ΔT ≈ 28°C. If the system impedance characterisation is too optimistic, I'm anticipating that the realised temperature rise could be as much as ΔT ≈ 45°C, which would be too hot to operate the switch at full capacity. In the case of this eventuality, I will either add more fans in serial to improve this performance (to an estimated ΔT ≈ 32°C at 24 CFM), replace the Sunon's with the Wakefield DC0402812J2B-3T0 (for an estimated ΔT ≈ 27°C), or add an additional fan to the ASIC as has been described in other successful fan mods.
For the ICX7250-48P, we're aiming for >60 CFM to stay within the ΔT=20°C - 25°C range. None of the fans I evaluated fall within this range. The closest was the Mechatronics G4028H12B2-RSR which with 3 fans in parallel generates 41.5 CFM at the typical 1U system impedance design point. If you were to use these fans, you would expect to see a temperature rise in the order of ΔT=35°C, which would likely push the switch into critical territory. Placing another 3 of these fans in series increases the total airflow to ~46 CFM, which improves things, but not enough to change things drastically. This still has a ΔT ≈ 32.5°C rise. Three of the Foxconn OEM fans in parallel only generate 68 CFM at the 1U typical impedance, so I'm hard pressed to imagine a quieter solution is available that satisfies the performance threshold, without adding more fans, larger fans (like the 120mm mods I've seen), or fans in different locations (like on top of the ASIC).
Having said that, as you can see there is a solution space to play around with if you don't need the maximum thermal capacity of the switch. If you're only using half the PoE load, then I suspect the comments about the ICX7250-24P will mostly apply.
As a final note, I hope that this has also made it obvious where there might be utility in going for very low noise, low CFM fans like the Noctua NF-A4x20. This type of fan has very low noise (14.9 dBA) and produces a maximum airflow of approx 5.5 CFM. As per the temperature thresholds chart above, ~5 CFM can cool up to 100W of heat generation with a temperature rise of ΔT=35°C. I would consider this the extreme outer range of performance, and would not trust this to an individual fan. In the interest of maintaining a temperature rise of ΔT=25°C, I would limit my usage of a single NF-A4x20 fan to applications less than 60W. This likely excludes many PoE switches. These fans also do not have a large static pressure rating, and Noctua haven't published any P-Q charts for them so it's difficult to know what the relationship looks like, but I would assume practically you will get less than 5 CFM of performance out of them in most applications. It's also worth noting that there are other reasons not to select these fans for the ICX7250-24P - there are minimum RPM thresholds that need to be satisfied so that the switch doesn't think that the fan has died; I've seen some reports that this has occurred with these fans.
Additionally, it's worth pointing out that another major deficiency in this analysis is the effective noise. All of this analysis has made assumptions based on the maximum sound pressure. Practically though, these fans are likely to be operating at some fractional speed, ideally at their most efficient around ~50%. Each of them will have unique noise profiles that may be better or worse, regardless of the maximum sound pressure value. They may have harmonics or whines that make them less tolerable, even if they are quieter. Unfortunately, the vendors didn't seem to publish much on this to draw insight from so in the absence of any personal experience this hasn't been treated as a decision point.
8. Selection and Recommendations
NOTE: Not all of the fans in these results have been tested. Use these at your own risk.
NOTE: You should come back to these recommendations after reading the Initial Results post, which highlights some issues with arranging fans in series.
- For the extremely noise conscious and with a mild to moderate PoE load
- 3x Sunon MF40201VX-1000U-G99 (32.3 dBA, estimated ΔT ≈ 28°C)
- Add additional 3 fans in serial if cooling performance insufficient for your needs (35.3 dBA, estimated ΔT ≈ 32°C)
- Replace fans with an alternative or add additional fan to ASIC if still insufficient
- For the moderately noise conscious, but likely to have a reasonable (but not full) PoE load
- Solution 1 (preferred)
- 3x Same Sky CFM-4020CF-195-342-20 (39.0 dBA)
- Add additional 3 fans if cooling performance insufficient for your needs (42.0 dBA)
- Solution 2 (if 1 not available)
- 3x Mechatronics MR4020H12B1-RSR (39.9 dBA)
- Add additional 3 fans if cooling performance insufficient for your needs (42.0 dBA)
- Solution 1 (preferred)
- For the moderately noise conscious, but likely to have a full PoE load with a lot of devices
- 3x Wakefield DC0402812J2B-3T0 (42.8 dBA)
- You shouldn't need to add any more fans to this; this should really be enough in most cases. However, if you add another 3 in series, you should be at ~90% of stock fan performance (45.8 dBA)
- Note that there have been reports that the Wakefield falls below the minimum RPM threshold in Speed 1
- For those who are not noise conscious at all and only want performance
- Add 3 more of the Foxconn fans in series
- Add 3 more of the Foxconn fans in series
Initial results showing the outcomes of my purchases are available in the Initial Results post
Resources
- Fan Curves Master Class with Greenheck
- Fan Curves Master Class Update!!
- Establishing Cooling Requirements: Air Flow vs Pressure
- Technical Note: Some Useful Fan Rules for Electronics Cooling
- Cybernetics Fan Performance Database
- DigiKey Brushless Fans
Edit 15/05/2026: Update fan table to include confirmed and unconfirmed functionality in the switch
Edit 26/05/2026: Update selection and recommendations to (a) include a disclaimer about the recommendations being theoretical and unvalidated, and (b) resolve typo erroneously recommending the Sunon MF40101VX-1000U-G99 (10mm depth and not assessed) instead of the Sunon MF40201VX-1000U-G99 (20mm depth, assessed)
Edit 08/06/2026: Add links to initial results post
Last edited: