MTP \ MPO fibre in new building

Notice: Page may contain affiliate links for which we may earn a small commission through services like Amazon Affiliates or Skimlinks.

psc

Member
Jun 30, 2019
74
27
18
I'm in the process of building & fitting out a new home office (etc.) which will also have our data room. I'm planning on running both LC pairs (10G now) and MPO (40G now, and easier to run now than later) between the rack room and the office (plus MPO between buildings). I'm somewhat comfortable with LC pairs, but (excepting shorter server\switch connections) I've not mucked about with MPO before. It's all going in trunking & conduit, so in theory I'll be able to re-pull later, but we all know how that works in practice.

1) Am I right in thinking that if I drop in 12-fibre OM4 I'm covered to at least 100G?

2) If I'm going to "terminate" to patch panel in the data room, and wall outlet in the office, is keystone coupler at both ends simplest?

3) MPO patch cables seem to be female-eneded. If so, it sounds like I'd need up-down keystone'd couplers at the ends, with male-male ends on the fibre run between. Is that right? What about polarity? Is there anything else I need to think about?

4) Does anyone have any idea how much space I'll need behind the keystone? I'm looking at a 40G MTP now, and the boot + bend radius seems like ~10cm; that's not going to fit inside any UK back-box, even with an angled outlet! I could print up a side-outlet faceplate for a double backbox (146x86mm), but it might look ****.

5) Am I being an idiot?
 
As an example to the statement above - when I ran 300m MTP cable to my shed, OS2 (12 fiber) was $1k, OM4(12 fiber) was $3.5k for the same spec and length. OS2 with MTP cassettes is the way to go and you can do any speed you want. Doing it with an MTP/MPO to LC cassette is probably the easiest because then you can just get 1m lc cable to your switch or servers. No need to terminate yourself.

If using MTP cassettes female will be fine, FS has a tutorial on the polarity and cable types. Type A -> OS2 -> Type AF to make it easiest.
 
  • Like
Reactions: psc and zunder1990
Dont do muti-mode, single mode only. 2x stands of single mode can do 10g/40g/100g/400g
exactly this.
It doesn't make any sense for new installations to use multimode.

Regarding the number of fibers to run: take the number of fibers you need now + some extra for backup, double that number and round that up to the next full dozen and at least go for a 2x12 strand cable.
SM cabling is dirt cheap, so just add more than enough spares and you don't have to touch that for the next 10-15 years (at least).

ALSO: If you have to go through several walls/floors where drilling new holes is a pain (e.g. brick walls and reinforced concrete) and/or you have to go through yet another cable duct every few meters, just install a microduct (e.g. 10/6mm or 12/8mm) and push your cabling through that. If for whatever reason you have to replace the cabling again, it's a matter of minutes instead of hours with the duct. I just did that for a connection from the basement to the living room, where we had to go through 5 walls (brick and box tile) and a steel reinforced concete floor and above cladded ceilings (permanently installed - not the easy-access types like in offices...) in 2 rooms.

You can use cabling that is pre-terminated on one side, but usually that's more expensive than to just use plain cabling and have someone splice it. You don't have to have all fibers terminated at once, so you can save a few bucks here (because splicing will amount for the largest part of the overall costs).

Also don't use MTP/MPO connectors directly on each end of that cabling (unless you really need *a lot* of MTP uplinks; hint: you don't). just use LC/MTP fanout patch cables for where you really need them but have the cable terminated to plain standard LC/UPC. Except for very special purposes you won't need more than 2 fibers for a single connection even for 100G and above with single mode. In the long run MTP will pretty much vanish except for maybe some inter-rack cabling...
 
  • Like
Reactions: bugacha and psc
Dont do muti-mode, single mode only. 2x stands of single mode can do 10g/40g/100g/400g

I'd discounted BiDi (which I think is what's needed for 40G over a single pair) on the basis of optics cost, but it looks like I can eBay a Cisco QSFP-40G-SR-BD (MM) or Juniper QSFP-40G-LR4-A for ~£25 at the moment. Might be the way to go; run a pair of MM and a pair of SM to each outlet and I'm covered on all fronts.


As an example to the statement above - when I ran 300m MTP cable to my shed, OS2 (12 fiber) was $1k, OM4(12 fiber) was $3.5k for the same spec and length. OS2 with MTP cassettes is the way to go and you can do any speed you want. Doing it with an MTP/MPO to LC cassette is probably the easiest because then you can just get 1m lc cable to your switch or servers. No need to terminate yourself.

If using MTP cassettes female will be fine, FS has a tutorial on the polarity and cable types. Type A -> OS2 -> Type AF to make it easiest.

Within building I'm only on ~15m runs, with FS pricing <$40 different for SM\MM MPO. I'll have a few 50m runs between different buildings, but I was planning OS2 there anyway.


I think I'm happily being talked out of MTP\MPO entirely!
 
Regarding the number of fibers to run: take the number of fibers you need now + some extra for backup, double that number and round that up to the next full dozen and at least go for a 2x12 strand cable.
SM cabling is dirt cheap, so just add more than enough spares and you don't have to touch that for the next 10-15 years (at least).

In the building, I'm hoping 2 fiber + 2 copper drops to each desk (mine + wife's) should be more than adequate. It'll all be in steel trunking\conduit, dedicated to network cabling, so (the idiot in me says) it should be safe enough once installed.


ALSO: If you have to go through several walls/floors where drilling new holes is a pain (e.g. brick walls and reinforced concrete) and/or you have to go through yet another cable duct every few meters, just install a microduct (e.g. 10/6mm or 12/8mm) and push your cabling through that.

It's all going in as the building is done, so no issues there. However, it might still be a sensible option, given it's going above a fixed ceiling and behind walls. I'll have to look into how much space I'll have in the trunking; I'm planning 50x100mm for network cables, but there's plenty of copper to fill it up. What's the bend radius on them like in practice?

You can use cabling that is pre-terminated on one side, but usually that's more expensive than to just use plain cabling and have someone splice it. You don't have to have all fibers terminated at once, so you can save a few bucks here (because splicing will amount for the largest part of the overall costs).

Again, I'd assumed pre-terminated was the only financially viable option, especially when I'll only be wanting a few drops done. I'm not sure yet how I'd find someone to terminate for me, but I'll have a think about it.
 
It's all going in as the building is done, so no issues there.
Then everything is going into conduits anyways, yes (or so I hope - at least that is the standard here for 30+ years...).
OTOH pulling relatively stiff fiber cables through those corrugated pipes can be a massive PITA, so adding microducts throughout the whole building might also be a sensible idea if it's a new building anyways. At least for horizontal cabling I'd definitely run some ducts that all run together at a dedicated electrics/data room in the basement. On a new building it's "now or never" to add all kinds of ducts into the wall - anything you want to add later involves either ugly surface-mounted ducts or a hammer drill, lots of dirt and ruined wallpapers and the risk of damaging existing ducts and cabling...

What's the bend radius on them like in practice?
Depends on the exact fiber type (G.652/G.657) and quality, but for plain standard G.652 you usually find for installation cabling, its around 10-15xdiameter. The problem isn't that it will break immediately (unless you actually kink the cable), but the signal will be dampened. For very short runs like in a building this isn't an issue if you have one or two tight bends - signal strength will still be plenty.
As a rule of thumb ~10cm bend radius is totally fine, down to 5cm also isn't a problem if you don't have multiple-km runs and several such tight bends. The bend should be somewhat supported at such a low radius though, i.e. the cable shouldn't be bent directly around a corner e.g. in surface-mounted ducts that are joined at 90° angles, or it will kink over time (or if someone pulls on one end).


Again, I'd assumed pre-terminated was the only financially viable option, especially when I'll only be wanting a few drops done. I'm not sure yet how I'd find someone to terminate for me, but I'll have a think about it.
For 2-4 fibers to some desks it might be a viable option (altough FS has become rather expensive IMHO...). But microducts aren't wide enough for LC connectors. There are pre-terminated cables available that only have some protective sleeve around a pre-crimped ferrule where you assemble the connectors after pulling the cabling, but haven't seen those for a while...
I'd use standard drop-cables which are extremely cheap and pre-terminated on one side. They are used for FTTH installations and hence widely available in various lengths. The other side can either be terminated by splicing on connectors or pigtails (usually in a splice box in the rack) or mechanical splice connectors. Yes, the latter ones have higher insertion loss, but at those short distances we're talking about within a small building, this is no issue.

Whatever variant you choose: DON'T let the cables just hang out of the wall to be plugged into a NIC or switch! (I've seen such botch-up plenty enough with copper and lately also with fiber...). Always install proper wall jacks (e.g. keystone) and use patch cables to the devices.
 
  • Like
Reactions: psc
My take is: LC duplex SM fiber will be supported for a very long time if for no reason than the amount of it that exists not only in buildings but also underground.

The best use of SMF MPO/MTP is as a breakout to LC pairs, since it's generally cheaper to get a single cable with many lines in it than run individual cables for each pair.
 
  • Like
Reactions: nexox and psc
I'd discounted BiDi (which I think is what's needed for 40G over a single pair) on the basis of optics cost, but it looks like I can eBay a Cisco QSFP-40G-SR-BD (MM) or Juniper QSFP-40G-LR4-A for ~£25 at the moment. Might be the way to go; run a pair of MM and a pair of SM to each outlet and I'm covered on all fronts.




Within building I'm only on ~15m runs, with FS pricing <$40 different for SM\MM MPO. I'll have a few 50m runs between different buildings, but I was planning OS2 there anyway.


I think I'm happily being talked out of MTP\MPO entirely!
We have very good luck with this optic XQX2502 KAIAM QSFP+40G-LR4 Lite OPTICAL MODULE NEW PULLS | eBay
40gb over 2x stands of single mode with an optic cost of $4

we use a ton of them at work, we always put them in a lag pair just in case we get a bad optic. so far a very low failure rate, we probably have about 200 of them in production.
 
  • Like
Reactions: nexox and psc
Then everything is going into conduits anyways, yes (or so I hope - at least that is the standard here for 30+ years...).
Yep. Salamandre steel trunking and 25mm steel conduit (bent as needed, any junctions via those circular conduit boxes).

Depends on the exact fiber type (G.652/G.657) and quality, but for plain standard G.652 you usually find for installation cabling, its around 10-15xdiameter.
I was more meaning the microduct; I've not worked with them before so I've no idea how flexible they actually are (without kinking!).

Whatever variant you choose: DON'T let the cables just hang out of the wall to be plugged into a NIC or switch! (I've seen such botch-up plenty enough with copper and lately also with fiber...). Always install proper wall jacks (e.g. keystone) and use patch cables to the devices.
You're preaching to the choir on that one :)

We have very good luck with this optic XQX2502 KAIAM QSFP+40G-LR4 Lite OPTICAL MODULE NEW PULLS | eBay
40gb over 2x stands of single mode with an optic cost of $4
The only eBay listing that'll ship to the UK wants 3x as much for shipping\duty as for the modules themselves, which makes them a lot less attractive. They're still half the price, but...

Edit: If I'm feeling lucky I could always risk AliExpress used for £7...
 
Last edited:
I was more meaning the microduct; I've not worked with them before so I've no idea how flexible they actually are (without kinking!).

They come in different variants - some are quite stiff and really require intention to get kinked and some are a bit softer and if pulled hard might kink at tight bends or corners. The huge advantage of the latter ones is, that they can be somewhat "pre bent" or straightened out by hand to e.g. directing them in a lowered ceiling to the next point where you can grab it. They are also easily held in place in a slot in the wall with a few clamps/wedges until they are covered in plaster.
The stiff ones fiercely want to remain in the shape they were stored on the spool, so they can be a PITA, but even builders with the poorest fine motor skills can install them without kinking (unless they really want to...).

I'd use the softer type for easier installation - the stiff ones are really for when you have to pull the tube over longer distances across various bends and corners.
Both variants can be connected with couplers, so you can patch them up if needed or if you damaged a part. At the room where those ducts all run together it might make sense to only leave 0.5-1m excess length and then use a couplers to add the final (and maybe softer) piece of duct that runs into the rack and the splice box. This simplifies installation and replacement of the cables, as you don't have to pull the whole cable through your rack.
 
  • Like
Reactions: psc
Supported ports: [ FIBRE ]
Supported link modes: 10000baseKX4/Full
40000baseCR4/Full
40000baseSR4/Full
56000baseCR4/Full
56000baseSR4/Full
1000baseX/Full
10000baseCR/Full
10000baseSR/Full

Just for your information Mellanox CX 3 non pro does not support LR4 optics

Supposedly what i wrote is not true see post below.
 
Last edited:
Supported ports: [ FIBRE ]
Supported link modes: 10000baseKX4/Full
40000baseCR4/Full
40000baseSR4/Full
56000baseCR4/Full
56000baseSR4/Full
1000baseX/Full
10000baseCR/Full
10000baseSR/Full

Just for your information Mellanox CX 3 non pro does not support LR4 optics

I'm using a CX354A with the AQOLBCQ4EDMA0878 LR4-lite optic. It doesn't list 40000baseLR4 as an option, yet it works fine. I don't place that much faith in the "modes" that a NIC does or does not claim to support.
 
Last edited:
  • Like
Reactions: nexox and rtech
Just for your information Mellanox CX 3 non pro does not support LR4 optics

Supposedly what i wrote is not true see post below.
I'm using a CX354A with the AQOLBCQ4EDMA0878 LR4-lite optic. It doesn't list 40000baseLR4 as an option, yet it works fine. I don't place that much faith in the "modes" that a transceiver does or does not claim to support.

I'm on a mix of CX-3 and SolarFlare cards; it's beyond me why the card needs to even know, let alone care, but I guess I'll be getting a couple of pluggables to check.
 
You can rent fusion splicers and otdr's for not _that_ much (like ~500/wk?). As long as you aren't doing ribbon the process is pretty easy. I agree with everyone else about just pulling os2 everywhere.
 
  • Like
Reactions: psc
In the building, I'm hoping 2 fiber + 2 copper drops to each desk (mine + wife's) should be more than adequate. It'll all be in steel trunking\conduit, dedicated to network cabling, so (the idiot in me says) it should be safe enough once installed.
2 fiber strands (so one duplex link)? 2 copper drops is one IP phone (if you're doing that) which might have a network extension jack, plus another drop for your computer.

I have a 100+ year old brick (inside and out) house and running cables is a pain. I've been here since the early 1990s, so things have gone from CAT 3 phone + thin coax Ethernet to MM fiber to SM fiber. New cables often went through existing holes drilled for earlier cables. I recently "bit the bullet" and drilled a bunch of new 1.25" holes which makes fishing pre-terminated fiber a lot easier. Those holes will probably fill up with cables eventually, too.
Again, I'd assumed pre-terminated was the only financially viable option, especially when I'll only be wanting a few drops done. I'm not sure yet how I'd find someone to terminate for me, but I'll have a think about it.
Unless you have a friend with a fusion splicer and some splice trays, pre-terminated is the way to go. I can buy a 30m SM "armored" LC/LC cable for only a little more than I'd pay for the connectors to do the job myself. If you need to go through small-diameter openings, get a cable with split LC connectors so you can "unzip" the fiber jacket and put one strand of the LC through the hole, then the other strand. You don't have to unzip the whole cable, just enough to put one connector through and enough additional so that you're not creating too tight a temporary bend radius when putting the other connector through.
 
  • Like
Reactions: psc
You can rent fusion splicers and otdr's for not _that_ much (like ~500/wk?). As long as you aren't doing ribbon the process is pretty easy. I agree with everyone else about just pulling os2 everywhere.

For 500USD/GPB/EUR you can even get a simple cladding alignment splicer (e.g. SignalFire AI-5 or 6); even core-alignment splicers like the SignalFire AI-9 can be found for 600-700USD/GPB/EUR e.g. during events on aliexpress.
For occasional splicing on sub-km runs these are absolutely sufficient and do the job (very well) - in fact in many countries the whole infrastructure was/is built with such machines. It's mainly in the US and parts of Europe where there's still a "religious cult" around insanely expensive gear like Sumitomo or Fujikura. Sure, they come with a sh*tload of certifications you might need for contract work with large companies/governments etc, but at the end of the day these machines all do the very same thing and can easily produce splices with <0.02dB loss; they don't have to cost as much as a small to mid-sized car for that...
I also own an AI-9 for occasional small splicing jobs @Home/work/friends/spare-time jobs that now has ~200 splices on it and not a single bad one yet.

But for doing a handful of splices once it still doesn't make sense to buy all the equipment... If you go multimode you might have to replace the cables every few years, but with singlemode you're settled for the next 10-20 years (or more...)
 
  • Like
Reactions: nexox and psc
I'm starting to get the impression that some of you think single mode might be marginally preferable :)

2 fiber strands (so one duplex link)? 2 copper drops is one IP phone (if you're doing that) which might have a network extension jack, plus another drop for your computer.

2 fiber drops + 2 copper drops. My desktop is already on fiber only, and if my wife gets one it'll have fiber one way or another within a week ;). So the copper is really just for IP Phone (which has passthrough) + laptop\RasPi\LicheeRV\etc. I could go 2 fiber + 4 copper, or even 4+4, but I feel like the odds of needing it is low enough that I'd just run a desktop switch. (Yes, I know I'm going to regret that sentence later!)

For 500USD/GPB/EUR you can even get a simple cladding alignment splicer (e.g. SignalFire AI-5 or 6); even core-alignment splicers like the SignalFire AI-9 can be found for 600-700USD/GPB/EUR e.g. during events on aliexpress.

Looks like I could get the Ai-9 for ~£315 (https://www.aliexpress.com/item/1005008571106630.html), but 4xLC pigtails seems nearly as expensive as a 15m pre-terminated cable so cost\ease\risk just doesn't add up for me.



Anyway.... 40G LR4 optics are due tomorrow, so if they're happy in both the switch (brocade) and nics (CX-3) I guess I'm running 2 SM drops to each spot.
 
  • Like
Reactions: bugacha
But for doing a handful of splices once it still doesn't make sense to buy all the equipment... If you go multimode you might have to replace the cables every few years, but with singlemode you're settled for the next 10-20 years (or more...)
At a museum I volunteer at, another one of the volunteers got a used semi-automated ribbon fusion splicer for a few hundred bucks on eBay from a seller in China. It worked surprisingly well (I was asked to bring my OTDR and check the splices). Their splicer actually produced better results than I've had presented to me as "pass" on some dark fiber I was leasing for my tri-state ring. Yes, it's harder to get good results on a 70km fiber run with multiple splice points, but when my OTDR reports a failure 300' from my launch point on a 70km run, I'm going to reject it and not even bother looking at the test results past that point.

But since it was ribbon splices,the volunteer had to get splice trays, fanouts, etc. But still a lot less expensive than having someone come out and do the splicing.

For low pair counts in a residence, pre-terminated is the way to go, as long as you can get the lengths you need - like extension cords and ropes, the piece you have is usually just a little too short or way too long. :confused:

There's enough SM fiber installed that technology will likely evolve to continue to allow the use of in-place SM fiber at ever faster speeds, rather than forcing rip-and-replace.
 
  • Like
Reactions: psc
Anyway.... 40G LR4 optics are due tomorrow, so if they're happy in both the switch (brocade) and nics (CX-3) I guess I'm running 2 SM drops to each spot.
You're just reminding me that the world is passing me by, at least for home use... I thought 10GbE was great. What's the use case for 40GbE to the desktop? Just curious, and "Because I can" is certainly a good enough answer. Each of my 10GbE desktops can do 600+Mbyte/sec continuous to my 10-year-old NAS boxes and I don't personally have a need for anything faster than that.